Honeywell R7284B No power after power outage
700635rhs
Member Posts: 1
in Oil Heating
Hello I have an oil burner that has no power to the controller. It will run if I jump the l1 to the b1.
it did this in the beginning of the season but just started working randomly. Any ideas?
it did this in the beginning of the season but just started working randomly. Any ideas?
0
Comments
-
So you have L1 constant power, and Limit, coming from B1 in the aquastat.
Anything in the primary diagnostics memory?
Do you have an electrical meter? Is there 120 volts across B1 and B2 in the aquastat?
What make and model aquastat?0 -
Hello @700635rhs,
If you have this type of Aquastat, It would not surprise me if the solder joints that connect the relay to the circuit board are failing.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0