Adding wood boiler
Hratchk
Hratchk Member Posts: 3
Adding wood boiler on my existing system. my system is only heating first floor on my main house. I would like to add other buildings to my new system.
    hot_rod Member Posts: 27,707
    what brand and model of wood burner do you have?
    will someone be available to keep it going in the event if a power outage, freeze protection can be a concern
  • Hratchk
    edited January 2024
    I am off grid. Wood boiler is Greenwood 100 at 100000btu. when I am not location LP boiler will take over.Existing system is on glycol.
    That is a bit of a finicky boiler to operate. A different approach to a gasification design boiler without a secondary chamber. It is a tube type boiler, tough to clean.
    They must have dry wood to prevent creosote formation, get a moisture meter.
    They must have return temperature protection, easily done with a thermostatic valve.
    You really need a buffer tank especially with all those small low temperature loads. I would plan on 250- 500 gallons of insulated storage. Firebox is fairly small, almost impossible to get an 8 hour burn out of them, especially at full fire.
    You need to burn them hot, a slow smoldering fire will create a creosote forming disaster.
    Some good operating info over at the hearth website from some actual users.
    With all that in mind I would suggest a building large enough to house the boiler and a buffer tank. With south facing roof, you could tie some solar thermal to that tank for DHW year around.
    Looks like you need at least a two temperature system, low temp for radiant, and some higher temp for the panel radiators. Looks like you have 2600 sq ft of radiant. If you had a. 25 btu/ sq ft load, the boiler is sized pretty close for you coldest days. It’s the shoulder season days where it gets tricky to heat with wood. So a large storage will allow you to build a large hot fire and coast through the day or evening. It also acts as the overheat protection.
    Here up is a rough sketch of how I did my system. A old 500 gallon lp tank on end for thermal storage. A 15 psi pressurized tank system.
    Wood boiler maintained the tank always at 160- 180.
    Solar would add to the tank anytime the sun was shinning, 5 collectors 4x8 size.
    The lp boiler would only heat the very upper part of the tank, about 35 gallons.so you always had a load for the solar or wood heat to bring the entire tank up
    I used a plate style heat exchanger on the tank to provide near endless hot water.
    When out of town, or sick of burning wood, about mid March😏, a control switched the lp on seamlessly.
    Snoop around the Hearth site for more user tips.
    What about hot domestic water, is that from this system also?
  • Hratchk
    Thank you for this info. Really appreciate it!