Circulator pump very hot
holograham
holograham Member Posts: 121
I assume this is not normal. Any thoughts on troubleshooting? My other pump is about 160 degrees (close to water temp). This one is 235+.
    EdTheHeaterMan Member Posts: 12,497
    edited January 2024
    Air bound? That is a water lubricated pump and the boiler water is inside that section of the pump, but the stator windings are between the water and the green metal case you are measuring the temperature of.
    Or the pump is stuck and you are just melting the windings on there.
    I'm guessing you have no heat on that zone?
  • holograham
    not sure if air bound - any way to check that?
    Yes believe no heat in zone. I turned it off so hopefully stops the circulator running.
    hot_rod Member Posts: 27,812
    Has it been running trouble and noise free recently?
    take a pic from back aways. So we can see if there are valves you can use to isolate and purge, or remove the pump for service
  • holograham
    Yes running trouble and noise free. I don’t know if it wasn’t heating recently as it had been warm but getting a cold streak now and it’s obviously not working.
    If every valve in that pic was turned iff you could remove the pump. Do so with the 4 bolts around the motor, 5/16” socket as I recall
    There should be a shutoff directly below the purge valve. Unless Im missing something, I don’t see a way to purge these zones?
  • holograham
    ok thanks. Then what? Replace it?
    The cost of a replacement cartridge may be as much or more than a complete new pump
    Shop for a new 007, or comparable replacement
    holograham
  • holograham
    Thanks!
  • Joe Mattiello
    Joe Mattiello Member Posts: 752
    Take an amp reading to see if the pump is running at or below name plate amps. That will tell what’s going on with pump. Pumps do run hot
    Joe Mattiello
    Taco Comfort Solutions
    HVACNUT Member Posts: 7,523
    Are these both radiant zones?
    Is there a radiant manifold?
    If it's radiant, and the other zone is radiant, is it possible the "hot" circulator was replaced in the past with a 007 that was readily available, and not the correct circulator? If both zones have the same flow rates and head, the zone 2 circulator looks like maybe a 0010.
    Zone 2 is also putting out 140°. High if radiant.
  • holograham
    Yes zone 2 putting out 140 on purpose - it goes to a room that is very cold so I bumped it up a little since we are going through a cold snap. Will move it down next week when temps go back to 30's (we are getting sustained single digit temps in Northern NJ now).
    Steamhead Member Posts: 18,696
    Maybe the mixing valve under the circ is bad, resulting in no flow to the circ?
    Consulting
    HVACNUT
  • holograham
    All - appreciate the comments - it turns out the pump was airlocked - fixed that and normal operations resumed!
  • MarkW66
    MarkW66 Member Posts: 4
    How did you remove the airlock?
    hot_rod
  • holograham
    I didnt remove it - my heating guy did the work. He hooked up some tubes to this special looking bucket and had some powered machine. I assume he circulated the water through the system somehow till he got the bubble out.
    Nailed it!
    holograham