Need help with Primary/Secondary Water Loops
josephny
Member Posts: 428
Several years ago I set up an IBC SFC-199 for DHW and a single zone under-floor hydronic heating.
I decided to add 5 additional zones upstairs and just built the system shown below.
I thought I had it all correct, but I can't get it to work. Using a Caleffi ZSR104 and a 103 (supply store did not have a 6 zone in stock) set up (I believe) as per the instruction manual, with an Ecobee on each zone, sure looks like the system is properly calling for heat.
But, I don't think there is any water flowing.
A thought that came up was whether I needed another pump somewhere on the secondary loop?
Can someone take a look at my design and tell me what's wrong?
Thank you!
Thank you!
Check valves in all the pumps!
purge valves somewhere?
Is there a pump inside the IBC?
piping is correct
Living the hydronic dream0 -
All valves checked (confirmed open)hot_rod said:Check valves in all the pumps!
piping is correct
Purge valves on each return line. Should I open them to release water and/or air?
Yes, IBC SFC-199 has internal primary loop pump.
Thank you for the piping confirmation.
I got the unit to fire up, but the heat does not circulate at all into the secondary loop. The primary loop hot side gets a little warm, but not like it is passing 160*F water through it's short copper pipes.
-1 -
Got it.
I was sort of hoping that air separator would take care of the initial big purge, but I see that was fantasy-thinking.
I thought the fill valve was an automatic device to bring the pressure up to a preset level? Do you mean mean the manual lever on top that I pull vertical to bring in more water should be left in the vertical position? Pressure would (I assume) rise to the house water pressure of mid-30's PSI. Is thank okay?
I did not use antifreeze initially and now am rethinking this decision. Can I simply open a return valve on one of the zones to remove existing pure water while pumping in antifreeze on the supply side?
No need to lift the lever on the fill valve, it should be pre set to 12-15 psi. Fast fill lever is just to fill and purge the first time.
Why the glycol consideration? Messy, expensive, maintenance prone, and some efficiency loss. In some cases a larger circ is needed.Bob "hot rod" Rohr
Living the hydronic dream1 -
I'm concerned about freezing. I have tons of sensors with alerts, but I am often far away from the location.
I thought it was cheap insurance.
Should I not use antifreeze despite 1200' of 3/4" pex running throughout the 3 story home carrying heating hot water?