Running out of hot water in shower in 5 min
tommydee
Member Posts: 18
Oil. Boiler. Domestic hot water tankless. Everything is newer 4 years
Should my aquastat have lower level settings?
I have high level but no control over low level
I am running
Carrier/Bryant bw5bah-140 boiler
With honewell L7224/L7248 Aquastat
I feel like hot water takes long and doesn't last long. Did my installer not install a correct aquastat?
Should my aquastat have lower level settings?
I have high level but no control over low level
I am running
Carrier/Bryant bw5bah-140 boiler
With honewell L7224/L7248 Aquastat
I feel like hot water takes long and doesn't last long. Did my installer not install a correct aquastat?
0
Comments
-
Hi, A couple of thoughts outside of the boiler... Have you tested to make sure there is no crossover between hot and cold lines? Is there a mixing valve that's allowing cold into the hot side when it shouldn't? A simple test might be to feel pipes supplying hot water to the house/shower and see just where things cool down. If all of that is good, then it's time to play with the boiler and possibly controls.
Yours, Larry1 -
I will look into crossover .. where would a mixing valve be?
And pipe access is limited.. it's a 2nd floor shower0 -
0 -
109A_5 said:Hello @tommydee, Is this a new, seasonal, or 4 year old problem ? Which Honeywell do you have L7224 or L7248 ? There is a difference. A picture of the Right side of the boiler may help.
Looks like a L7248
Is that the right aquastat for my set up? I would think I should have setting for LL
0 -
Just one shower, or all the faucets are acting up in 5 minutes?0
-
Yes, that is a high limit only aquastat. If you have a tankless coil, you need the L7224 or any equivalent triple acting aquastat.
When the tankless was added, the supplier and installer should've known better. It should be changed at no cost to you... unless it was you who installed it.
P.S. I love the pipe clearance for the swing out door. Awesome.
P.P.S. There's 3 firing rates for that boiler. Does the heat load demand 120K BTU's on a design day? That's a lot. You (a qualified tech) might be able to knock it down to the BW5BAH-105 firing rate and save a few bucks.
0 -
Is there no hot water holding/storage tank? A setup like that in my area would typically have a minimum of a small circ pump plumbed between coil and electric water heater. Lots of consistent temp hot water.0
-
HVACNUT said:Yes, that is a high limit only aquastat. If you have a tankless coil, you need the L7224 or any equivalent triple acting aquastat.
When the tankless was added, the supplier and installer should've known better. It should be changed at no cost to you... unless it was you who installed it.
P.S. I love the pipe clearance for the swing out door. Awesome.
P.P.S. There's 3 firing rates for that boiler. Does the heat load demand 120K BTU's on a design day? That's a lot. You (a qualified tech) might be able to knock it down to the BW5BAH-105 firing rate and save a few bucks.
And yeah, I noticed that too.. I did get it knocked down after fighting with the company that I ordered an energy star rated boiler the -140 wasn't so they ordered a kit with a nozzle and a baffle or some other stuff to knock down to -105 and made it 85% efficient.
That's for noticing that0 -
Keep in mind different firing rates require different set ups-nozzle, pump pressure, Probably a different head and a low fire baffle…and of course a complete combustion test.HVACNUT said:…There's 3 firing rates for that boiler. Does the heat load demand 120K BTU's on a design day? That's a lot. You (a qualified tech) might be able to knock it down to the BW5BAH-105 firing rate and save a few bucks.
There was an error rendering this rich post.
0 -
Hello @tommydee,
Do you have an ELL — External Low Limit (L7248L only) ? Where does that ZR wire go to on your unit ?
A picture of the Right side of the boiler may help. The pipes and stuff on the right side near the rear of the boiler.tommydee said:I will look into crossover .. where would a mixing valve be?
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
109A_5 said:Hello @tommydee, Do you have an ELL — External Low Limit (L7248L only) ? Where does that ZR wire go to on your unit ?
I will look into crossover .. where would a mixing valve be?
A picture of the Right side of the boiler may help. The pipes and stuff on the right side near the rear of the boiler.0 -
The ZR wire goes to this little guy... ohhhh is this an external low limit control???
0 -
It's hard to see but is the low limit set at 140? When I had a domestic coil I had to have mine set to 160 for a sufficient amount of water in the winter. I had a triple aquastat that was set at 180h and 160l.0
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 921 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements