How to purge air from radiant heat system

emetz51
emetz51 Member Posts: 2
Hello, first time in here, I was hoping someone could help me. I have an EFM pk 500 oil fired boiler. Its old was in the house when we moved in only this past year has it given us problems. The thing is driving me crazy with the air in the radiators. I was hoping someone would be able to walk me through purging the air out and tell me if theres anything I should replace thats allowing all that air to get in the first place.

Comments

  • hot_rod
    hot_rod Member Posts: 23,405
    is is there a pressure gauge on the boiler?
    12-15 psi is what you want 

    The brass air vent, is the cap loose?
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • emetz51
    emetz51 Member Posts: 2
    Hot_rod the cap on the brass vent above the x tank is loose. Boiler pressure is around 12 currently.
    if I wanted to go ahead and purge the air from the radiators, what steps would I take. Ive watched videos Im just afraid I let water out and somehow screw it up then im out heat till someone can come fix it. Im trying to learn for myself.
  • neilc
    neilc Member Posts: 2,854
    can you show us a radiator, both ends,
    and a wide shot of the boiler showing the circulator, and zone valves if applicable
    known to beat dead horses