Furnace Mis-firing on and off

jebigham
jebigham Member Posts: 1
I have a 20+ year old Lennox oil fired hot air furnace. This is the 2nd time in 3 years it chugs like a car firing on and off. Furnace is serviced every year. Last time a Honeywell control panel was replaced. Any ideas why again? Attached video cloud link.

https://share.icloud.com/photos/056wAmfes8dS4WS2MHRYqCm_w

Comments

  • SuperTech
    SuperTech Member Posts: 2,460
    I'm not sure but that seems dangerous. You should shut it down until your service provider can get there. Ask them to install a modern primary control with interrupted ignition. 

    Now that I think about it I've seen the Beckett AFII burner you have do that when the ignition transformer cables to the electrodes are damaged and arcing against the burner.
    STEVEusaPAMaxMercy
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,545
    edited December 2023
    The Primary control model number R8184M is the problem. This is a problem in the control flame sensing circuit. I am not a big fan of that control. Can you tell me the model number of your Lennox furnace so I can look up the wiring diagram? You need to upgrade to an electronic primary control. The problem is that the R8184M has a 40 VA transformer that other components on your Lennox furnace use. So the standard electronic primary controls like the Carlin ProX 70200 will not be an exact wire for wire replacement.

    With your Lennox wiring diagram I can offer your technician the necessary upgrade in order to replace that Dinosaur primary control with something that will not fail in the way your control has done 2 times in the last 2 years.

    EDIT: I have upgraded a furnace like this in the past. I just need the wiring diagram for your furnace to let you know how.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    MaxMercy
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Agree with the above. While checking wiring for a loose connection, I’d also take a look at the high limit, fan/limit.
    To me if it were just flame dropout, or coupling slipping, I’d expect the burner to lock out.

    There was an error rendering this rich post.

  • HVACNUT
    HVACNUT Member Posts: 6,382
    Same as above. Either faulty contacts in the M control, or something is preventing TT from staying closed.
    Can you take the cover off the electric to the left of the burner (Shut off the power first) and post a pic of what's there? I'm pretty sure there's a control board in there so I don't understand why the M is even being used. 

    Is there air conditioning? If yes, in the zone panel, is Rc,Rh jumped, or is there a separate wire to each? 
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,545
    Looked all over for the Lennox with the the R8184M in the wiring diagram. Could not find it.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • Big Ed_4
    Big Ed_4 Member Posts: 3,050
    edited December 2023
    Jump out TT and maintain a watched electrical meter on black and white leads on the primary control ( red button ). If burner runs steady check your thermostat circuit . If the primary receives a steady voltage and relay still flickers replace the primary .If there is no AC on the furnace you can replace with a cheaper non 40VA primary control... If you notice the meter flicker you will need to check deeper ..

    There was an error rendering this rich post.