Riello Flame sensor F3 F5
BDR529
Member Posts: 310
in Oil Heating
Noticed the new black flame sensors have little to no change in resistance when checked with a meter. I have 3 of them on the bench can they all be bad? all sensing light at start up.
The old white sensors show a good change in resistance.
What am i missing?
The old white sensors show a good change in resistance.
What am i missing?
0
Comments
-
The black one is a photodiode; it generates current in the presence of light. Eliminates the use of cadmium.To learn more about this professional, click here to visit their ad in Find A Contractor.1
-
New Flame Sensors
Riello has launched new flame sensors for use with all of its domestic oil-fired burners that are covered by EU Directive 2011/65/EU (Restriction of the Use of Certain Hazardous Substances in Electronic and Electrical Equipment), which comes into force in July 2019.
As a result, Riello RDB, 40 and Gulliver models now require new cadmium-free photocells within the flame sensors if replacement is required. For RDB models the correct replacement depends on whether an analogue or digital control box is in use.
EU Directive 2011/65/EU is designed to prevent certain hazardous substances from entering the production process, resulting in the introduction of these new cadmium-free technologies within the flame sensor
Where are you located? You may not need the Black one. there is a chart that you need to look at to determine if the new black is compatible with your burner's control
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
-
I'm in Mass.
Riello 40 with 20132573 eye is what matches and I have. Dose not like it.
Well, that answers the odd readings.0 -
It takes the current generated and electronically converts to resistance so it's backward compatible. The black cover is hinged, you can pop it open and take a lookBDR529 said:Since it generates then the 530se should be a different control to accept the change in photo cell?
To learn more about this professional, click here to visit their ad in Find A Contractor.1 -
So it is a diode, thought it was a fancy new window.
Hope the directive stays in the EU.0 -
"Cadmium and its compounds are highly toxic and exposure is known to cause cancer. It is primarily associated with human lung, prostate, and kidney cancers, and recently pancreatic cancer. It has also been associated with cancers of the breast and urinary bladder."
I would expect cad cells to go away here as well eventuallyTo learn more about this professional, click here to visit their ad in Find A Contractor.0 -
-
Do you actually touch anything hazardous on a cad cell or is it all contained?
There was an error rendering this rich post.
0 -
BDR529 said:Never had the urge to crack open a cad-cell eye and give it a good snort or fire it up my back door. I'm a responsible service tech. Apparently it has been a problem so they took it away from us. Oh man! What violation did they perform on the T-87 thermostats!!0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements