Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
burnham steam boiler # IN7SNC-ME2
Dan_43
Member Posts: 57
Comments
-
Yes ,the yellow wire, coming from the transformer would be the common . Add a 3amp fuse on the blue to protect the transformer from shorts .
There was an error rendering this rich post.
0 -
Thank you for confirming my thinking. And why do you think I would need a fuse on the blue, now because I'm tapping the yellow?0
-
Hello @Dan_43,
The Blue wire is the 24 VAC Hot wire leaving the transformer, the Yellow wire is grounded.
It is just good practice and you are adding more load and wires to the system, more potential for issues.
If your new toy has a meltdown the fuse may save the transformer.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements