Lochinvar "Dis"ConXus Issues ?

Derheatmeister
Derheatmeister Member Posts: 1,573
edited December 2023 in THE MAIN WALL
We have 33 Lochinvar ConXus interface modules installed for some of our customers and have had serious issues with them over the years...
Anyone else want to share their experiances..
:#

Comments

  • Derheatmeister
    Derheatmeister Member Posts: 1,573
    Has anyone seen the following issues or is this just isolated to us?
    1. SH Controlling sensor which was allotted to the outlet disappears.
    2. Modulation Factor which was set to 40% disappears.
    3. HW System Pump Mode which was set to "force off" disappears / resets itself to "Call for heat"
    4. Ramp delay which was set to "Ramp up" reverts to "No delay".
    5. The one that really concerns us is the SH 1 setpoint which was programmed to 155F magically "Reprogrammed itself" to 120F which could have resulted in a Frozen house.
    Other issues are present and i will add these as i find them. :s
  • hot_rod
    hot_rod Member Posts: 22,833

    Has anyone seen the following issues or is this just isolated to us?
    1. SH Controlling sensor which was allotted to the outlet disappears.
    2. Modulation Factor which was set to 40% disappears.
    3. HW System Pump Mode which was set to "force off" disappears / resets itself to "Call for heat"
    4. Ramp delay which was set to "Ramp up" reverts to "No delay".
    5. The one that really concerns us is the SH 1 setpoint which was programmed to 155F magically "Reprogrammed itself" to 120F which could have resulted in a Frozen house.
    Other issues are present and i will add these as i find them. :s

    Have you spoken with Shamrock or Lochinvar directly? Are their software upgrades to fix bugs?
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mattmia2
    mattmia2 Member Posts: 10,422
    Is this an issue with software losing a connection but still saying it saved settings anyway?
  • Derheatmeister
    Derheatmeister Member Posts: 1,573
    mattmia2 said:

    Is this an issue with software losing a connection but still saying it saved settings anyway?

    Yes.. that happens as well.
  • Derheatmeister
    Derheatmeister Member Posts: 1,573
    hot_rod said:

    Has anyone seen the following issues or is this just isolated to us?
    1. SH Controlling sensor which was allotted to the outlet disappears.
    2. Modulation Factor which was set to 40% disappears.
    3. HW System Pump Mode which was set to "force off" disappears / resets itself to "Call for heat"
    4. Ramp delay which was set to "Ramp up" reverts to "No delay".
    5. The one that really concerns us is the SH 1 setpoint which was programmed to 155F magically "Reprogrammed itself" to 120F which could have resulted in a Frozen house.
    Other issues are present and i will add these as i find them. :s

    Have you spoken with Shamrock or Lochinvar directly? Are their software upgrades to fix bugs?
    Yes I have discussed this with both Harrold from Lochinvar and Shamrock Sales..
  • Derheatmeister
    Derheatmeister Member Posts: 1,573
    edited December 2023
    Just talked to another contractor here in Summit County Colorado (Eric F..... from Al......) that also had a bad experience with the "New" ConXus.
    Once they hooked it up to the boiler the screen of the Knigth just went Crazy/showed all kinds of weird simbols..Lochinvar was not helpfull in this case and they decided to returned it for credit to the source it came from and are seriously contemplating using Lochinvar products again .They probaby also lost the customer confidence in the the Lochinvar products !
    Again this is product has had many issues over the years, customers are not getting what they paid for and contractors are left without support or just lip service (Stop complaining and just Go Away)...Shame on you Lochinvar for not addressing a faulty product !
    How would you feel if this happend to you ?