Noise from inside water heater
gyrfalcon
Member Posts: 179
When we run the water, hot or cold, from any fixture and then stop the flow, there is a noise that happens from inside the hot water heater, it almost sounds like a noise from inside a submarine as it goes deeper, like metal creaking with changing pressures. Has anyone heard this type of noise from a water heater before? It’s not a kettling noise from from what I can tell.
Slant Fin Galaxy GG100(1986) , 2 zone hot water baseboard, T87 Honeywell thermostats.
0
Comments
-
What is your water pressure in the home? Does the relief valve on the tank ever drip?
excessive pressure can make noise as will sediment in the tank when the burner is runningBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Pressure is 60lbs. Expansion tank 60lbs.Sound does not happen when firing , just when water flow stops. Relief valve does not dripSlant Fin Galaxy GG100(1986) , 2 zone hot water baseboard, T87 Honeywell thermostats.0
-
Hi, @hot_rod nailed the common causes of noise in a tank. Is there any way you can record the sound and post it here? With that, we can probably narrow it down.
Yours, Larry1 -
do you have a PRV on the domestic?
I have one at work that howls once in a whileknown to beat dead horses0 -
Slant Fin Galaxy GG100(1986) , 2 zone hot water baseboard, T87 Honeywell thermostats.0
-
Anybody??I tried using a mechanics stethoscope on the water tank jacket and Expansion tank seems loudest at the jacket. I also shut off the cold inlet to the tank and the noise was not present then.Slant Fin Galaxy GG100(1986) , 2 zone hot water baseboard, T87 Honeywell thermostats.0
-
Hi, I just get a 404 note saying the audio file is not available. So, noise has something to do with pressure. Does it happen only when flow stops? Have you put a pressure gauge on the tank drain and then run water to see what the gauge tells you? If you see large pressure differences, it could be a pressure reducer on your main line that is failing.
Yours, Larry0 -
I’m trying to get the sound recording file to load but I think the format is not compatible. I’ll try again laterSlant Fin Galaxy GG100(1986) , 2 zone hot water baseboard, T87 Honeywell thermostats.0
-
Yes. Noise only happens when flow stops.I’ll check pressures tonightSlant Fin Galaxy GG100(1986) , 2 zone hot water baseboard, T87 Honeywell thermostats.0
-
trying again.
Slant Fin Galaxy GG100(1986) , 2 zone hot water baseboard, T87 Honeywell thermostats.0 -
I’m thinking maybe you are hearing the PRV react to the shut off of flow. A pressure gauge would confirm the PRV is not over pressurizingBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I attached a pressure gauge to my water heater drain. Initial reading was 70 psi. I observed the needle while water was being used in the kitchen and bathroom. Pressure would sometimes go to 50lbs and then around 60. Finally resting at 70lbs again.Slant Fin Galaxy GG100(1986) , 2 zone hot water baseboard, T87 Honeywell thermostats.0
-
70 psi is fairly high pressure. PRVs are typically factory set to 45 or 50 psi
but that pressure shouldn’t be causing a water heater tank to flexBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Do you think the Ty-D-Bowl man might have gotten lost in the piping on his way to clean your toilets?
That could be his motor boat making all that racket
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
@EdTheHeaterMan, I appreciate your humor, but no Ty-dee bowl boats in my house.I left the gauge on the tank last night and checked it this morning. Almost 80 psi. And it’s holding there while someone is in the shower. If I recall the water pressure and domestic expansion tank are set at 60 lbs.
i just disconnected the gauge and then reconnected and now reads 55.Slant Fin Galaxy GG100(1986) , 2 zone hot water baseboard, T87 Honeywell thermostats.0 -
Not sure whether it is sound from pressure differential or possibly sound of heat expansion of materials as hot water flows out of the tank?0
-
Hi, Maybe I'm making it up, but in the recording I thought I heard water running and then as soon at it was shut off, the creaking started. As a test you could dial down the PRV to 50 psi and change the charge in the expansion tank as well. If you get adequate flow at the reduced pressure, it certainly will put less stress on the tank. I'd watch pressure and see if it creeps up over time. If so, that's a sign of a failed PRV.
I normally get that creaking noise at higher pressures though. Are you pretty confident in the gauge you're using?
Yours, Larry0 -
It is the Death Rattle , Mineral build up with the sound of energy breaking through .
There was an error rendering this rich post.
0 -
The tank is a Richmond 50 gal. LP atmospheric. Approximately 4 -5 yrs old .I have adjusted the pressures- water and expansion tank (system drained off and isolated)
to about 55 psi. Gauge seems accurate . I could try another I suppose.Noise still present just as water flow stops.This is limestone county so lots of calcium in the water. Maybe there is some mineral build up.Thanks for everybody’s input. Y’all are grrreat!Slant Fin Galaxy GG100(1986) , 2 zone hot water baseboard, T87 Honeywell thermostats.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 912 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements