Noise from inside water heater

When we run the water, hot or cold,  from any fixture and then stop the flow, there is a noise that happens from inside the hot water heater, it almost sounds like a noise from inside a submarine as it goes deeper, like metal creaking with changing pressures.  Has anyone heard this type of noise from a water heater before?  It’s not a kettling noise from from what I can tell. 
Slant Fin Galaxy GG100(1986) , 2 zone hot water baseboard, T87 Honeywell thermostats. 

Comments

  • hot_rod
    hot_rod Member Posts: 23,515
    What is your water pressure in the home? Does the relief valve on the tank  ever drip?

    excessive pressure can make noise as will sediment in the tank when the burner is running
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • gyrfalcon
    gyrfalcon Member Posts: 179
    edited December 2023
    Pressure is 60lbs.  Expansion tank 60lbs.  
    Sound does not happen when firing , just when water flow stops. Relief valve does not drip
    Slant Fin Galaxy GG100(1986) , 2 zone hot water baseboard, T87 Honeywell thermostats. 
  • Larry Weingarten
    Larry Weingarten Member Posts: 3,614
    Hi, @hot_rod nailed the common causes of noise in a tank. Is there any way you can record the sound and post it here? With that, we can probably narrow it down.
    Yours, Larry
    Intplm.
  • neilc
    neilc Member Posts: 2,868
    do you have a PRV on the domestic?
    I have one at work that howls once in a while
    known to beat dead horses
  • gyrfalcon
    gyrfalcon Member Posts: 179
    https://jmp.sh/s/Ck88tIpRZjNani2DvOoA
    Lets see if this audio link works
    Slant Fin Galaxy GG100(1986) , 2 zone hot water baseboard, T87 Honeywell thermostats. 
  • gyrfalcon
    gyrfalcon Member Posts: 179
    Anybody??  
    I tried using a mechanics stethoscope on the water tank jacket and Expansion tank seems loudest at the jacket. I also shut off the cold inlet to the tank and the noise was not present then. 
    Slant Fin Galaxy GG100(1986) , 2 zone hot water baseboard, T87 Honeywell thermostats. 
  • Larry Weingarten
    Larry Weingarten Member Posts: 3,614
    Hi, I just get a 404 note saying the audio file is not available. So, noise has something to do with pressure. Does it happen only when flow stops? Have you put a pressure gauge on the tank drain and then run water to see what the gauge tells you? If you see large pressure differences, it could be a pressure reducer on your main line that is failing.

    Yours, Larry
  • gyrfalcon
    gyrfalcon Member Posts: 179
    I’m trying to get the sound recording file to load but I think the format is not compatible.  I’ll try again later 
    Slant Fin Galaxy GG100(1986) , 2 zone hot water baseboard, T87 Honeywell thermostats. 
  • gyrfalcon
    gyrfalcon Member Posts: 179
    Yes. Noise only happens when flow stops. 
    I’ll check pressures tonight 
    Slant Fin Galaxy GG100(1986) , 2 zone hot water baseboard, T87 Honeywell thermostats. 
  • gyrfalcon
    gyrfalcon Member Posts: 179
    trying again.
    Slant Fin Galaxy GG100(1986) , 2 zone hot water baseboard, T87 Honeywell thermostats. 
  • hot_rod
    hot_rod Member Posts: 23,515
    I’m thinking maybe you are hearing the PRV react to the shut off of flow. A pressure gauge would confirm the PRV is not over pressurizing
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • gyrfalcon
    gyrfalcon Member Posts: 179
    I attached a pressure gauge to my water heater drain. Initial reading was 70 psi.  I observed the needle while water was being used in the  kitchen and bathroom. Pressure would sometimes go to 50lbs and then around 60. Finally resting at 70lbs again. 
    Slant Fin Galaxy GG100(1986) , 2 zone hot water baseboard, T87 Honeywell thermostats. 
  • hot_rod
    hot_rod Member Posts: 23,515
    70 psi is fairly high  pressure. PRVs are typically factory set to 45 or 50 psi

    but that pressure  shouldn’t be causing a water heater tank to flex
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,541
    Do you think the Ty-D-Bowl man might have gotten lost in the piping on his way to clean your toilets?



    That could be his motor boat making all that racket

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • gyrfalcon
    gyrfalcon Member Posts: 179
    edited December 2023
    @EdTheHeaterMan, I appreciate your humor, but no Ty-dee bowl boats in my house. 

    I left the gauge on the tank last night and checked it this morning. Almost 80 psi. And it’s holding there while someone is in the shower.  If I recall the water pressure and domestic expansion tank are set at 60 lbs. 

    i just disconnected the gauge and then reconnected and now reads 55.  
    Slant Fin Galaxy GG100(1986) , 2 zone hot water baseboard, T87 Honeywell thermostats. 
  • psb75
    psb75 Member Posts: 912
    Not sure whether it is sound from pressure differential or possibly sound of heat expansion of materials as hot water flows out of the tank?
  • Larry Weingarten
    Larry Weingarten Member Posts: 3,614
    Hi, Maybe I'm making it up, but in the recording I thought I heard water running and then as soon at it was shut off, the creaking started. As a test you could dial down the PRV to 50 psi and change the charge in the expansion tank as well. If you get adequate flow at the reduced pressure, it certainly will put less stress on the tank. I'd watch pressure and see if it creeps up over time. If so, that's a sign of a failed PRV.

    I normally get that creaking noise at higher pressures though. Are you pretty confident in the gauge you're using?

    Yours, Larry
  • Big Ed_4
    Big Ed_4 Member Posts: 3,050
    It is the Death Rattle , Mineral build up with the sound of energy breaking through .

    There was an error rendering this rich post.

  • gyrfalcon
    gyrfalcon Member Posts: 179
    The tank is a Richmond 50 gal. LP atmospheric. Approximately 4 -5 yrs old . 

    I have adjusted the pressures- water and expansion tank (system drained off and isolated)
    to about 55 psi.  Gauge seems accurate . I could try another  I suppose. 
    Noise still present just  as water flow stops.  

    This is limestone county so lots of calcium in the water. Maybe there is some mineral  build up.  

    Thanks for everybody’s input.  Y’all are grrreat! 