I need to replace a corroded and leaky globe valve that's part of a hydronic baseboard system for my girlfriend's grandparents. I've replaced a section of leaky pipe on our home system before, and done other plumbing work, so I think I have a pretty good handle on what I need to do.
It's an old single zone system, and doesn't have a purge valve, so I'm planning on installing that as well.
When I purged the zones on my house after replacing the leaky fitting, I put the zone valves for each zone in bypass. For this system, there's just a taco cartridge circulator. Am I right in thinking there's no need to do anything like the bypass on the zone valve so that water will still flow through this with the system powered off, so that I can purge the system? Water just will flow through from the pressure from the incoming water so I can purge it?
I need to replace a corroded and leaky globe valve that's part of a hydronic baseboard system for my girlfriend's grandparents. I've replaced a section of leaky pipe on our home system before, and done other plumbing work, so I think I have a pretty good handle on what I need to do.
It's an old single zone system, and doesn't have a purge valve, so I'm planning on installing that as well.
When I purged the zones on my house after replacing the leaky fitting, I put the zone valves for each zone in bypass. For this system, there's just a taco cartridge circulator. Am I right in thinking there's no need to do anything like the bypass on the zone valve so that water will still flow through this with the system powered off, so that I can purge the system? Water just will flow through from the pressure from the incoming water so I can purge it?
0
Comments
-
Valve that needs replacing
0 -
There's no bleeders on the convectors or radiators?
Also, the circulator is pumping into the expansion tank. Not good. The circulator should be downstream of the PONPC.
It also looks like the piping splits into 2 loops. If you pipe in a purge station, you'll need to be able to isolate the loops so you can alter flow through one or the other.1 -
The pictures indicate that your girl friends parents, have a different design from the one at your house. You should Just Dump that girlfriend. Problem solved!
But seriously, If you are going to attempt that repair, you should understand the difference. Can you post some pictures of the radiators/baseboards/convectors, or whatever heaters are in the rooms.Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
HVACNUT said:There's no bleeders on the convectors or radiators?
Also, the circulator is pumping into the expansion tank. Not good. The circulator should be downstream of the PONPC.
It also looks like the piping splits into 2 loops. If you pipe in a purge station, you'll need to be able to isolate the loops so you can alter flow through one or the other.
There are bleeders, I'll post pictures of the baseboards below.0 -
EdTheHeaterMan said:The pictures indicate that your girl friends parents, have a different design from the one at your house. You should Just Dump that girlfriend. Problem solved! But seriously, If you are going to attempt that repair, you should understand the difference. Can you post some pictures of the radiators/baseboards/convectors, or whatever heaters are in the rooms.
1 -
Here are some pictures of the baseboards, and the bleeder valves. Not sure when the last time any of these things were turned, but perhaps I should just do it that way. Was just worried with the age of the system that something would break or leak and I'd have a bigger issue on my hands.
0 -
@ererer
The picture shows the globe valve needing replacement. Why is there always something in the way? Figures!?
Anyway. No zone valve so no bypass in the circ. You are correct.
Install the purge on the return with the ball valve below the boiler drain close to the boiler.
From your described experience, it sounds like you know the rest of what to do.
I would install the purge even with the coin vents on the rads. The system will be down anyway to change the bad valve so why not?
Go for it.1 -
Intplm. said:@ererer The picture shows the globe valve needing replacement. Why is there always something in the way? Figures!?
You can see how much the pipe was pushed up from where it originally was.
1
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements