This a bull head t?

Went into the basement of a local home renno to look at the old boiler the local plumber is working on (you guys have made me infinitely curious).  I couldn't see any vents on the mains so I asked where they were and he said they weren't needed because it's a 2-pipe system 🤔

Anyway, here are some pics of the old boiler and progress   The trol is set under 2 psi which is nice.  They're also adding at least 3 or 4 large rads to the system.  Haven't met the owner yet, really glad he didn't just rip it out.


Bryant 245-8 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains.  26 radiators heating up 3800sqf.

Comments

  • Steamhead
    Steamhead Member Posts: 17,330
    The vents are in the second pic. Two radiator traps are piped between the ends of the steam mains and the dry return. We call these "crossover traps" since they route air from the steam mains into the dry return. The large device in that pic is a "vent trap" which may or may not have a vacuum check screwed into the top- this is where the air actually leaves the system. From what I can see this is probably a Dunham Vapor system.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    SuperTechGrallertguzzinerdMad Dog_2
  • KC_Jones
    KC_Jones Member Posts: 5,805
    The header is wrong for sure. It's colliding and no swing joints. Why is there a hot water boiler gauge on there? Hopefully they did the heatloss for the new radiator sizing and connect them right, I have doubts based on what I see.

    They may have kept it, but still have the wrong contractor working on it.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,297
    @KC_Jones

    Must be one of those really old steam and water systems :):)
    KC_Jones
  • guzzinerd
    guzzinerd Member Posts: 263
    KC_Jones said:
    The header is wrong for sure. It's colliding and no swing joints. Why is there a hot water boiler gauge on there? Hopefully they did the heatloss for the new radiator sizing and connect them right, I have doubts based on what I see. They may have kept it, but still have the wrong contractor working on it.
    There are no steam contractors anywhere near us, which is why I like to sneak in and post pics here for the experts.  

    How can you tell there are no swing joints under all that insulation?  Asking for myself.

    Thanks 
    Bryant 245-8 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains.  26 radiators heating up 3800sqf.
  • KC_Jones
    KC_Jones Member Posts: 5,805
    "There are no steam contractors anywhere near us"

    Apparently they disagree with you, I mean look at those pics, they are obviously a steam contractor...

    Because the elbows are going straight into the header and facing each other. There should be an offset to allow for some expansion and contraction as shown in the second picture below.




    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
    guzzinerd
  • guzzinerd
    guzzinerd Member Posts: 263
    edited December 2023
    Thanks for the swing explanation. 

    A local plumber is acting as the steam contractor.  Another plumber had been maintaining mine until I bought the place and had to undo a lot of their work with the help of this forum and Dan's books.
    Bryant 245-8 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains.  26 radiators heating up 3800sqf.
  • clammy
    clammy Member Posts: 3,155
    They installed two elbows right on the outlet of the boiler which served as there swing joint . I ve seen many older boiler piped similar and they worked fine no wet steam mainly due to the large steam chest area internally as in comparison to a modern boiler which really solely depends on correct near boiler piping to do the work of slowing down the exiting velocity and drying the steam in doing so . It usually is a lot of work to repipe to a modern steam header arrangement for a modern boiler .i would image a new properly installed boiler would drastically cut gas consumption . Thanks for the pics that one looks pretty much un knuckled headed as of yet but give it time . Not
    Peace and good luck clammy

    R.A. Calmbacher L.L.C. HVAC
    NJ Master HVAC Lic.
    Mahwah, NJ
    Specializing in steam and hydronic heating

  • guzzinerd
    guzzinerd Member Posts: 263
    clammy said:
    They installed two elbows right on the outlet of the boiler which served as there swing joint . I ve seen many older boiler piped similar and they worked fine no wet steam mainly due to the large steam chest area internally as in comparison to a modern boiler which really solely depends on correct near boiler piping to do the work of slowing down the exiting velocity and drying the steam in doing so . It usually is a lot of work to repipe to a modern steam header arrangement for a modern boiler .i would image a new properly installed boiler would drastically cut gas consumption . Thanks for the pics that one looks pretty much un knuckled headed as of yet but give it time . Not Peace and good luck clammy
    Very interesting, thanks.  Our area hasn't had any steam guys in decades.  I have a feeling many boilers are piped this way as this is the second one I see like this still operating.
    Bryant 245-8 2-pipe steam in a 1930s 6-unit 1-story apt building in the NM mountains.  26 radiators heating up 3800sqf.