Beckett R7184b

Eadacorp
Eadacorp Member Posts: 1
Turns on starts pumping (no flame) , no oil out of the pump to nozzle ….  Solenoid not being powered. Does show 120v for a millisecond but goes to zero.  The Solenoid has no ohms .  It’s the control bad or just solenoid 

Comments

  • Steamhead
    Steamhead Member Posts: 17,744
    Probably the control. But if you have a suitable cord, you can power the valve directly with 120V to make sure.