Beckett R7184b
Eadacorp
Member Posts: 1
in Oil Heating
Turns on starts pumping (no flame) , no oil out of the pump to nozzle …. Solenoid not being powered. Does show 120v for a millisecond but goes to zero. The Solenoid has no ohms . It’s the control bad or just solenoid
0
Comments
-
Probably the control. But if you have a suitable cord, you can power the valve directly with 120V to make sure.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0