Your help please
RayWohlfarth
Member Posts: 1,656
Ok I remember @DanHolohan talked about never using a one pipe air vent on a two pipe radiator with a steam trap. I can't remember why and can't find the reason for it. Someone asked me why and I sounded like my father. "Because you don't" What happens when you install an air vent on a 2 pipe radiator? Thanks
Ray
Ray
Ray Wohlfarth
Boiler Lessons
Boiler Lessons
0
Comments
-
-
-
Yeah..Ray...see that often when guys are trying to get two-pipe-Steam Trap Radiators 🔥 and don't address the bad traps & poor main venting. It is also wasted $$ as good Vents are $$$ now....times that by a whole apartment building! Mad Dog 🐕
1 -
Thanks @Mad Dog_2 I love that I learn something new everyday in our industry
Ray Wohlfarth
Boiler Lessons2 -
Oh yeah..well you do more than your fair share of edifying us! Mad Dog 🐕1
-