Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Your help please
RayWohlfarth
Member Posts: 1,645
Ok I remember @DanHolohan talked about never using a one pipe air vent on a two pipe radiator with a steam trap. I can't remember why and can't find the reason for it. Someone asked me why and I sounded like my father. "Because you don't" What happens when you install an air vent on a 2 pipe radiator? Thanks
Ray
Ray
Ray Wohlfarth
Boiler Lessons
Boiler Lessons
0
Comments
-
-
-
Yeah..Ray...see that often when guys are trying to get two-pipe-Steam Trap Radiators 🔥 and don't address the bad traps & poor main venting. It is also wasted $$ as good Vents are $$$ now....times that by a whole apartment building! Mad Dog 🐕
1 -
Thanks @Mad Dog_2 I love that I learn something new everyday in our industry
Ray Wohlfarth
Boiler Lessons2 -
Oh yeah..well you do more than your fair share of edifying us! Mad Dog 🐕1
-
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements