ARCO Ideal 28 Hot Water Boiler Age and Info

offdutytech
offdutytech Member Posts: 154
Go for a no heat call turn the corner and see this beauty. ARCO Ideal 28, house was built in 1880s homowner said. Anyone have more info on this boiler? It looks nice but has a few issues and we are going to quote replacement, boss dosnt want the liability for repair.  Contemplating two smaller boilers vs one large one due to stock and the pipe configuration. 
WMno57

Comments

  • JUGHNE
    JUGHNE Member Posts: 11,248
    Did you get a chance to run it and clock the meter?
  • Steamhead
    Steamhead Member Posts: 17,312
    50% efficient at best on gas or oil. Bet the new boilers cut their gas usage in half.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • offdutytech
    offdutytech Member Posts: 154
    It was not running when I got there. Burner was in rough shape. Customer is ready upgrade, From some info that I found the coal rating was 1500-1650 ( this was from a later model 1908). Can't remember if that's all I need to find an aprox BTU rating. We are doing a load calc, i'm more curious on the rating of the boiler. A little more investigation on the piping to determine if I'm going to put smaller boilers or one large one in with narrow access to basement. 
  • mattmia2
    mattmia2 Member Posts: 10,702
    A mod con usually does well on a gravity conversion and will fit down the stairs. It wouldn't be unusual to buy a larger coal boiler so that more coal could be stacked on the grates so it didn't have to be stoked as often.
  • JUGHNE
    JUGHNE Member Posts: 11,248
    The size of the orifice in the burner and a guess at the gas pressure to it out of the valve (3.5"?) might get you in a range.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,251
    I don't know what they heated that house with in 1880 but I would bet anything that is the first and only boiler installed in that house.

    I always wondered how they picked up those horizontal sections and set them on the push nipples. Maybe they brought the horse down stairs. That boiler will be a nice removal job.
    JUGHNEoffdutytechmattmia2
  • offdutytech
    offdutytech Member Posts: 154
    I will be heading back to the job to take more measurements and see if I can get more info off the gas train retrofit. A Viessman  Vitocrossal was my first thought or divide the right side supply / return to its own boiler and do the same with the left. Going to have to run the numbers for the customer
  • JUGHNE
    JUGHNE Member Posts: 11,248
    Look for the open top expansion on the top floor or in the attic, that will have to be capped.

    Also as far as dividing the zones up for left and right, I have found that they are usually stacked up. Some piping to the right might do 2-3 floors above it.
    And the same for the left.

    So not a matter of splitting up that easy.
    mattmia2
  • offdutytech
    offdutytech Member Posts: 154
    I didn't make it up to the attic just yet to look for the tank. At first glance that looks like what they did
  • mattmia2
    mattmia2 Member Posts: 10,702
    Unless the house is enormous a single modcon will likely heat it just fine. Tee the supply and returns together, put a balancing valve somewhere in each branch, size the bear boiler piping based in the heat loss, look for orifice plates on the top radiators which you may need to move to the lower radiators. You don't need a tone of flow. Put a magnetic dirt separator on the return.
    offdutytech
  • Alan Welch
    Alan Welch Member Posts: 270
    Looks like it was almost time to replace the rusty plug in the relief valve. There might be a date on the pressure gauge ...not that it would coincide with the boiler age. Don't throw that out, a few people collect them.
    GGross
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,251

    Just imagine, no low water cutoff, a strap on aquastat and it survived for over 100 years. Probably was Coal fired for much of its life. I would guess maybe 1950s on the gas burner.

    Put a Carlin gas burner in it and run it for another 100 years. LOL
    WMno57SuperTechdelcrossv
  • WMno57
    WMno57 Member Posts: 1,408
    JUGHNE said:

    Also as far as dividing the zones up for left and right, I have found that they are usually stacked up. Some piping to the right might do 2-3 floors above it.
    And the same for the left.
    So not a matter of splitting up that easy.

    That's the way my 1916 gravity hot water piping is. Someday, I might replace my boiler. At that time it would be nice to put the second floor on a separate zone. But that would involve more re-piping. Only 4 radiators on my second floor, so they might get their own pex runs.
  • offdutytech
    offdutytech Member Posts: 154
    Worked up a quote for a Viessman Vitocrossal 300 with taps for indirect direct domestic option. Talking to the customer about his gas bills 😮. They are ready to change after we compared the efficiency of the equipment vs what they had.
  • reggi
    reggi Member Posts: 523
    Measuring for rating. Heights, pipe sizes, etc and do the math
    One way to get familiar something you know nothing about is to ask a really smart person a really stupid question
    offdutytech
  • sopcopotoptop
    sopcopotoptop Member Posts: 25
    Hi offdutytech! I’m new to this but I have a 4-28-W ARCO Ideal Series 28-1B round boiler I just picked up. The slice door was all busted up but the rest of the boiler is in amazing shape. Did you end up removing this boiler and changing out for your customer? If so, would the slice door be available? Thanks for your post and the time. Scott.