Oil Boiler short cycling
Just_Jack
Member Posts: 5
in Oil Heating
I have a new-to-me home and a Weil-McLain Oil fueled boiler (heat only) which was installed in 2018. It runs all the time, even when the thermostat is not calling for heat nor is the circulator on. I realize the boiler is designed to keep water hot and "at the ready" for when the thermostat calls for it, but it seems to not hold heat for longer than 15 minutes. For example, I have timed it to cycle on for about 2 minutes to get up to temperature. Then it holds the high temp for about 4 minutes before dropping a degree every 30 seconds after that until it reaches low temp and fires back up. I have had the service repair company look at this 3 separate times, and they keep telling me it's operating as it should. It is burning oil like crazy, I can't imagine this is energy efficient.
Any help is appreciated
Any help is appreciated
0
Comments
-
What you have described is a WTGO boiler operation. that is used for domestic hot water. You mentioned that you have a heat only boiler. That should be the WGO boiler, that does not maintain temperature as you describe. Which boiler do you have and are you sure you are not using it for Hot Water.
Picture of boiler and piping around it
Picture of the label with the model number
This is what I'm talking about. WGO v. WTGO
Looking for your reply.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Yes, it is heat only. The model is Weil-McLain WGO Gold Series 3. I have hydronic baseboard radiators, and an electric hot water heater.0
-
Someone has an extra wire connected somehow that is turning the burner on when it does not need to be. Then the heat is thermosyphoning through the home to drop the boiler temperature. If it was originally installed to maintain temperature, the installer would have installed a check valve to keep the heat in the boiler. I will bet that there is no such check valve and there is a wiring or control problem that is keeping the burner operating on the short cycle.
Can you post the pictures I requested?
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
@Just_Jack
You boiler should not be running when the thermostat is not calling. Sound like you have an issue.
How is the heat in the house? Does it stay steady or is it over heating.0 -
@EdTheHeaterMan
Thank you, that is quite helpful. Here is a photo of the setup as you requested. It was taken when the boiler was off.
0 -
-
-
It is clear that the installer has some things to learn. This leads me to believe that he has made some mistakes that are not obvious from this picture. Look inside the control to see if the wires are set up like this
No wires are connected to ZC or ZR
The dial for the low limit should be set to OFF
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
-
-
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements