Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Boiler with compression tank, want to add B&G Airtrol fitting.

2»

Comments

  • hot_rod
    hot_rod Member Posts: 23,392
    That's quite the offset piping :)

    I think the relief valve should be mounted in a vertical position?
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    OldBoiler65
  • leonz
    leonz Member Posts: 1,339

    Just to update you all. I finally got a chance to plumb the B&G Airtrol into my boiler properly with 3/4" pipe. It's been working great so far for a week. I'd say this has to be the best this boiler has worked since new. Thanks again for all the help and suggestions. Here is a couple pictures of how I piped it to the tank.

    ------------------------------------------------------------------------------------------

    Good morning OldBoiler65,

    Bravo, congratulation's to you for an excellent installation and repair to your boilers air management system that is plumbed within its existing piping risers that will provide you with trouble free air management.

    Seeing the flanged gasketed pipe connections in your basements boiler piping illustrates true craftsmanship and thought regarding how your heating system was designed and installed.

    Gaskets for flanged piping are still made and available, do not let anyone tell you these gaskets are not available as they are made by the A.W. Chesterton Company of Groveland, Mass., which has a nationwide distributor network.

    As long as the larger air bubbles and microbubbles can escape the boiler steam chest they will waddle up the riser pipe to the ATF-12 Airtrol valve and the cool denser water in the base of the steel compression tank will fall, drop, sink back to the boilers steam chest waving so long to the rising air bubbles that are riding the hot water highway to the ATF-12 Airtrol valve.

    Thanks for bringing sanity back to your homes heating system that will provide you smooth even quiet heating and eventually no air bubbles to your heating plant.

    OldBoiler65
  • OldBoiler65
    OldBoiler65 Member Posts: 29
    hot_rod said:

    That's quite the offset piping :)

    I think the relief valve should be mounted in a vertical position?

    I agree, I thought it would be alright for now since the manual for the boiler shows the relief mounted horizontally.
  • OldBoiler65
    OldBoiler65 Member Posts: 29
    @leonz Thank you very much! Yes, it is a very nice system that was installed around 1920. The American Standard G-210 boiler was installed in 1965 to replace the original coal boiler. I brought it back from the dead after it had sat for possibly 20 years not working. Then I found that I could not get the air out no matter what I did. After browsing the internet, I found out about the Airtrol and with much help from this forum I found it had some issues with the piping. So far, I'm really happy with it. The boiler hasn't been this quiet or heated this well since I restarted it in 2021.
  • leonz
    leonz Member Posts: 1,339
    Yes!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!

    Thank the dead men, gas law, hydrodynamics, Mr. Holohan, the fine members of the forum and Bell & Gossett, Bell & Gossett which also makes hydraulic control valves.


    Enjoy the heat.
    OldBoiler65