DIY Adding Outdoor Reset to Munchkin 140M
SENorthEast1895er
Member Posts: 84
there's already a 13 yr old post on here with almost the same title, but without answers to my questions.
I’ve got a 140M with Vision 1 system and, for some reason, the previous owners didn’t install an OR. I bought the sensor and am looking to wire it.
Two questions:
I still need the female pins to add the wire to the Molex connector. I got a crimper with a variety pack of pins, but they’re too large. Does anyone know what size connector I’ll need?
For wire: I was planning on using T-stat wire. Will that be within spec?
thanks.
I’ve got a 140M with Vision 1 system and, for some reason, the previous owners didn’t install an OR. I bought the sensor and am looking to wire it.
Two questions:
I still need the female pins to add the wire to the Molex connector. I got a crimper with a variety pack of pins, but they’re too large. Does anyone know what size connector I’ll need?
For wire: I was planning on using T-stat wire. Will that be within spec?
thanks.
0
Comments
-
Why don't you just see if HTP still has replacement sensors ? https://htproducts.com/literature/lp-102.pdf
You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330 -
I bought the sensor already, from Jupiter Supply. It doesn’t come with a wire. Same listing as this one here: https://boilerpartsunlimited.com/products/7250p-319
EDIT: yea, annual you linked to specifies that both the wires and the sensor come with the Vision 1 control system, neither of which the previous owners seem to have left laying around.
edit again: here i thought the vision 1 system was a separate control board. but now im finding a new, open box vision 1 systems that’s just the wires and sensors. so… can someone explain to me what the difference between the vision 1 system and the 900-series Munchkin controllers is?0 -
Vision 1 is indeed just a set of wires and sensors. You plug into the existing 900-series Munchkin controller.
Well, all this info is in that pdf linked by Rich_49 above.0 -
yea, i guess im just dense. thanks.0
-
Doesn’t the sensor connect to the light green wires with wire nuts?8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
i don’t have the wires yet, but I do have a sensor i bought separately. it has no wires to wire-nut to.0
-
-
great. thats about what i figured. this should be -retry easy once it gets here.0
-
Am I correct in my understanding that, without using the indirect water heater sensor, the Vision 1 is just going to supply my hot water heater with reset-temp water?
Looking closer, it looks like my hot water and heating zone valves wires all got connected to the same T-stat wire for the boiler. So the boiler doesn’t know the difference.
I had hopes that I could just install the indirect water sensor and the Vision would recognize the call, without the need for a separate, indirect circ. But 1) my Triangle Tubes Phase III doesn’t even have a place to install it and 2) posts on here say you definitely need a circ for the indirect (waiting to hear back from htp about that) and to follow the piping diagrams (which would require me to add an indirect circ and move the main circ from supply side to return side).
Really bummed that this ODR isn’t a simple setup. The house was pretty cozy for the week before the warm weather led to a cold shower.
edit: my piping matches the “retrofit” example in the munchkin 925 140M etc install manual. which it doesn’t look like theresa a comparable version in the vision 1 install guide.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 918 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements