Identify 2 pipe steam radiator supply valve
Jdot
Member Posts: 2
Recently had a new Steam boiler installed. I took on the task of installing new Tunstall capsules for the Warren Webster traps. I also had a few valves with broken handle stems and wondered if I might be able to find rebuild kits or if its even worth rebuilding them. They seem to have these screws that thread into the sides of the valve. Images attached. Thank you.
0
Comments
-
From the looks of it that has an adjustable inlet orfice which would have been set to limit the amount of steam feeding into the radiator . You may find it difficult and expensive to replace w orificed valves . If unable to locate you can install standard steam angle valves and get blank orifice plates from turnstall and drill out the blank plates and install . Or just install standard steam angle valve and see if you have issue w balance and over heating . I ve ran into instances where it created issues relating to over heating and distribution .
Peace and good luck clammyR.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating1 -
What is the problem with the valve that you have . You normally don't use the shut off .
There was an error rendering this rich post.
0 -
-
Didn't american radiator make the ones with the screwdriver adjustment in the side?
https://heatinghelp.com/news-and-media/dead-men-tales/the-model-k-mystery/1 -
You nailed it, Matt. Those are from an Arco Model K system. Maybe someone added traps to it because they didn't understand the orificing principle?mattmia2 said:Didn't american radiator make the ones with the screwdriver adjustment in the side?
https://heatinghelp.com/news-and-media/dead-men-tales/the-model-k-mystery/All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
On the radiators they have Warren Webster 02h traps and Warren Webster 522hb traps that connect the drips at the end of the mains back to the returns that are then pitched back to the boiler room. I put 2 gorton #2s and a Hoffman 75 at the dry return just before it drops down to the wet and into the Hartford loop. Based on the pipe fitters blueprint for my home it originally had a receiver and pump/vacuum instead of relying solely on gravity back when it was coal.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements