Taco 219 swetchek
iizbor3d
Member Posts: 40
I have these taco flow check on all 3 zones that seem to have never been replaced. The top seems to be tightened all the way down, assuming fully closed. If I slightly try to open them water starts to come out. Is there a possibility they impede flow and are overworking my circulators? Can they be removed since the circulators have flow checks?
0
Comments
-
When they are screwed down they act as a flow check which is a weighted check valve. They let water through only if the circulator is running. Originally used on boiler that had a tankless water heater to not allow flow when running for DHW or on boiler with multiple circulators and multiple zones.
If you want to just open them and leave them in place try that.0 -
Unfortunately the slightest turn to open causes them to leak from the top. I'm sure whatever gasket is there has been completely deteriorated. I guess they should be replaced or are the circulator flow checks enough to prevent ghost heating?0
-
-
Great thank you!0
-
-
Joe Mattiello said:Flow check in circulator is much better choice for one directional valve. Less pressure drop, and better performance for your pump.Perhaps you can take the check out, and replace with a pipe plug.1
-
I was going to mention Ghost Flow. That may happen on the zone closest to the boiler. Since they are not blocked, and the only moving part is still moving, I would leave well enough alone. But if you do decide to try one of the zones. Try the one with the longest horizontal run before it turns up to the first radiator.
By the Way, that leak is from a packing nut. You can reduce the pressure on the boiler so little or no water leaks then add some packing under that nut. That way you can back the valve to full open, then tighten the packing nut to stop the leak. once the valves are open and you pressure the system, you can test for ghost flow without removing them.
See the diagram here https://s3.amazonaws.com/s3.supplyhouse.com/manuals/1351084254823/85085_PROD_FILE.pdfEdward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
We still see ghost flow sometimes. It's hit and miss even with integral checks on pumps. We still use the current flo checks from Taco on many jobs.
Tim0 -
EdTheHeaterMan said:I was going to mention Ghost Flow. That may happen on the zone closest to the boiler. Since they are not blocked, and the only moving part is still moving, I would leave well enough alone. But if you do decide to try one of the zones. Try the one with the longest horizontal run before it turns up to the first radiator. By the Way, that leak is from a packing nut. You can reduce the pressure on the boiler so little or no water leaks then add some packing under that nut. That way you can back the valve to full open, then tighten the packing nut to stop the leak. once the valves are open and you pressure the system, you can test for ghost flow without removing them. See the diagram here https://s3.amazonaws.com/s3.supplyhouse.com/manuals/1351084254823/85085_PROD_FILE.pdf0
-
If you do decide to replace them, consider a hydronic spring check
Flo checks add a lot of restriction to a circuit, equal to about 140’ of tubeBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements