Crown AWR series boiler.

Foremost
Foremost Member Posts: 1
Hello everyone, just recently purchased a Crown AWR series boiler. Wold like to add 4 zones like our old galaxy boiler using Taco ZVC 404-4 zone control. Problem is, there is no aquastat relay on this boiler to tie into. The wiring instructions don't cover that. Does anyone know the proper connections to tie into on this boiler? Thank you.

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,495
    Need a lot more information. Are you zoning with circulators or zone valves? Are you adding more zones or reconnecting what you have?
  • kcopp
    kcopp Member Posts: 4,472
    Should be able to hook the end switch from the ZVC to the TT connections at the wires in the boiler.
    Foremost
  • Steamhead
    Steamhead Member Posts: 17,387
    kcopp said:

    Should be able to hook the end switch from the ZVC to the TT connections at the wires in the boiler.

    This. The Aruba/AWR uses an integrated Honeywell control instead of the usual aquastat relay. Hook up your zone valve controller XX Main to TT on this control.