In a hydronic system, should the circ pump come before or after the exp tank?
jeremypbeasley
Member Posts: 19
Space is super tight as I rebuild a 100 year old cast iron radiator system into multiple zones. The old circ pump sat between the exp tank and the boiler. I'd prefer to keep it that way, but I've read some places that you want it after before air in the lines can burn up the pump. Is that actually a risk?
Any reason OPT B won't work?
I welcome any other critiques to my drawings and overall setup, too!
Any reason OPT B won't work?
I welcome any other critiques to my drawings and overall setup, too!
0
Comments
-
The circulator should be pumping away from the expansion tank. You could use a tee to get it there if you have to. There are also vertical versions of air separators and dirt separators that can help you accomplish that. If the circulator is pumping in to the expansion tank, the tank will absorb some of the pressure differential that the circulator has created instead of it being used to push the fluid through the system. It will also reduce the pressure at the inlet to the circulator making cavitation more likely.0
-
Consider one if the electronic ECM delta P circulators. The work nicely with zone valved
The expansion tank could be mounted anywhere as long as it connects into the piping near the pump inlet
It dies nit need to be below the air purger, so you could use a vertical purger, tee the tank into the line before the circ
with a low pressure drop boiler like that, the expansion tank could connect into the return at the boiler also
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 912 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements