Cement lined chimney will low stack temp be a problem

We had a new burner installed for better dependability replacing a 40 + year old power burner but the new one has a stack temp at <350 degrees F at the breaching and the cement lined chimney goes up 40 ft thru a cold garage. My concern is possible condensing in the boiler or enough condensing in the chimney to detiorate the lining until it fails  the boiler is a fire tube scotch type cica 1965 low pressure steam 
Any thoughts, thank you

Comments

  • Big Ed_4
    Big Ed_4 Member Posts: 3,019
    A chimney running up though the garage is not bad . North standing outside chimney really is the worse , A liner could not hurt . Size it to the new equipment would be best . A way to see if you really need a liner , on a cool day check the condensate leaving the chimney . There should be a space between the chimney and the condensate ..

    There was an error rendering this rich post.

  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Are you sure you’re not underfired?

    There was an error rendering this rich post.

    SuperTech
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,470
    If your net stack temp stays above 330 you should be ok.
  • Big Ed_4
    Big Ed_4 Member Posts: 3,019
    edited November 2023
    Scotch Marine boiler is very efficient ... The original owner knew and paid for it .

    There was an error rendering this rich post.

  • Blackoakbob
    Blackoakbob Member Posts: 252
    It is in a commercial  building and a commercial grade prefab chimney  sorry I  didn't  elaborate  more and a wet back scotch style boiler 
  • Blackoakbob
    Blackoakbob Member Posts: 252
    This new burner is the type that tunes it's  combustion by O2 varying gas and combustion air independently and modulates from high to low output by steam pressure my concern is too efficient (83%) for the old equipment chimney and boiler

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,470
    @Blackoakbob 83% should be fine in a normal chimney especially with steam
    Blackoakbob
  • Big Ed_4
    Big Ed_4 Member Posts: 3,019
    Do you mean the burner controls the proper O2 for level of combustion ? That's cool

    There was an error rendering this rich post.