Replacing an old condominium thermostat
thank you in advance for all the help.
I'm living in a condominium that has old thermostats (pic below):
The management can only replace them with the following ones and they charge 120CAD each?!
https://hsbuild.com/storage/product-pdfs/HVA50_Specifications.pdf
I asked if a "digital" one could be installed but didn't quite understand why they are not supported. They mentioned that tenants who did try to replace with a newer ones had controls inverted or something like that.
Could you please help me on how to connect something more modern, i would like to get something like this in the worst case scenario:
https://www.homedepot.com/p/Honeywell-Home-Round-Non-Programmable-Thermostat-with-1H-Single-Stage-Heating-CT87K/100476730
or even NEST if there is a way to connect it, but some 'digital' version with the scheduling temperature options would be just enough.
Comments
-
Might be a Series 20 control circuit. Some digital thermostats do support this, but have to be specifically programmed to do so.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Agree with @Steamhead, it looks like Series 20, power open, power close.
The Honeywell T4 Pro would work but must be programmed for that setup.See note 5.1 -
Thank you so much for the help!
When you say programmed, is that a simple setting/configuration I would have to select in settings or it requires more than that?
Are these the ones you are thinking of:
https://www.amazon.ca/Honeywell-TH4110U2005-Programmable-Thermostat-Digital/dp/B075ZMQWMP/ref=sr_1_1?hvadid=604601316364&hvdev=c&hvlocphy=9000976&hvnetw=g&hvqmt=e&hvrand=9246723686341355441&hvtargid=kwd-398976636184&hydadcr=27855_14574558&keywords=honeywell+t4+pro&qid=1699205521&sr=8-1&ufe=app_do:amzn1.fos.b06bdbbe-20fd-4ebc-88cf-fa04f1ca0da8
https://www.amazon.ca/H1ywell-Home-Programmable-Thermostat-Th4110u2005/dp/B082MPRJNW/ref=sr_1_6?hvadid=604601316364&hvdev=c&hvlocphy=9000976&hvnetw=g&hvqmt=e&hvrand=9246723686341355441&hvtargid=kwd-398976636184&hydadcr=27855_14574558&keywords=honeywell+t4+pro&qid=1699205521&sr=8-6
0 -
@HVACNUT @Steamhead could you please give me just a bit more of an assistance
Turns out the red wire doesn't do anything, it is not connected. So I thought this might be pretty simple, but it turns out it is not. I got the T4 Pro and tried different ways to connect.
So the fact to start with is if I disconnect the thermostat - the pipe is running hot through the condo. Neighbor tells me this is kind of a safety measure and they intentionally build it like this so in case of an power outage - heating will still work. It is somehow inverted. This is exactly how T4 Pro works now when connected, it is turning it on when it should turn it off and vice versa. I also tried to connect the wires opposite way but it is not helping.
0 -
So the Red wire isn't connected to anything.
What's the black and white wires connected to? Can we see?
What are you connecting at the T4, R+W or R+Y ?
I don't want to say without knowing what the thermostat wiring is connected to, but it sounds like a spring open, power close valve if it's only 2 wire.
If it is, then it should be R+Y and note 5 for the ISU.
0 -
-
-
@HVACNUT many thanks for the comment.
I don't really understand the note 5, what is ISU? I see three modes on the thermostat menu, Heat, Cool and OFF. There is nothing more in the Menu except from clock setting and similar. Again, thanks a lot for the help!!
Here is how it looks right now, it is basically acting inverted (turns on when it should turn off):
0 -
-
If you went with a honeywell TH6110D1021 your could set up for heat only in setup, radiant heat. Then in wire diagram for thermostat they show for zone valve Normally open type, use Y terminal to close. That's what it looks like to me. So any time a call for heat, power is removed to zone valve which allows valve to open. Then when heat is satisfied the Y terminal gets power and closes zone valve. Look at 4th down diagram on attached, left side to see what it references. Looks like might fit the bill.1
-
bokerman said:@HVACNUT many thanks for the comment. I don't really understand the note 5, what is ISU? I see three modes on the thermostat menu, Heat, Cool and OFF. There is nothing more in the Menu except from clock setting and similar. Again, thanks a lot for the help!! Here is how it looks right now, it is basically acting inverted (turns on when it should turn off):1
-
bokerman said:@HVACNUT YOU NAILED IT! I don't know how to thank you enough. No one in this condominium knows how to set this up, I've been living here for 9 now. Please let me know if there is anyway I can contribute to anything that would make some difference important to you.1
-
Thanks again for the help!mattmia2 said:If it is a normally open valve then you would need a professional t-stat that can be programmed to open the contacts on a heat call and close the contacts when the call ends. You could also use a regular t-stat with a relay and a 24 vac wall wart. That would let you power a "smart" t-stat too.
0 -
Couple of owners were talking about that an invertor is necessary but luckily there is a simple solution with the config @HVACNUT provided.mattmia2 said:Could you get a good picture of the markings on the valve? If it is a normally open valve you can either get a t-stat that supports that or you could put a relay at the valve that inverts the action of the t-stat since you have access to the transformer at the valve.
0 -
Thank you for the post. I believe this is what worked but only with T4 Pro: Wiring R+Y and doing Step 5 (Step 5 was Setting to Radiant heat (200 to 5) and number of stages to 0 (220 to 0). There were couple if T4 Pro for 15-20$ each on Facebook Marketplace, I couldn't be more happy.tim smith said:If you went with a honeywell TH6110D1021 your could set up for heat only in setup, radiant heat. Then in wire diagram for thermostat they show for zone valve Normally open type, use Y terminal to close. That's what it looks like to me. So any time a call for heat, power is removed to zone valve which allows valve to open. Then when heat is satisfied the Y terminal gets power and closes zone valve. Look at 4th down diagram on attached, left side to see what it references. Looks like might fit the bill.
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 912 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements