This formula determines the mix temperature of two flows into, or out of a tee.
It helps demonstrate how fixed flow adjustment comes into play for boiler return protection.
T mix= (T-hot x T flow) + (T-hot = T flow)
÷
F-hot + f-cool
Keeping in mind what goes into a tee must come out of a tee, flow wise.
These examples show a 12 gpm flow split evenly between two inlet flows.
If a boiler starts at an ambient 68F and return fluid is 68F, within minutes a properly sized boiler could add maybe 20∆ to the supply. So blending 88SWT with 68 return = 78°
If the boiler was up to temperature, say 160F, blending the return 68 = 114°
If the boiler could supply a constant 180F, and the load could increase to 88F, uoou mix would be 132°
When the return gets up to 160F, 180SWT the return to to the boiler is 170.F
So return is blending up, dropping boiler efficiency a bit compared to a 160F return, that you would see if the system was running a 20∆.
It helps demonstrate how fixed flow adjustment comes into play for boiler return protection.
T mix= (T-hot x T flow) + (T-hot = T flow)
÷
F-hot + f-cool
Keeping in mind what goes into a tee must come out of a tee, flow wise.
These examples show a 12 gpm flow split evenly between two inlet flows.
If a boiler starts at an ambient 68F and return fluid is 68F, within minutes a properly sized boiler could add maybe 20∆ to the supply. So blending 88SWT with 68 return = 78°
If the boiler was up to temperature, say 160F, blending the return 68 = 114°
If the boiler could supply a constant 180F, and the load could increase to 88F, uoou mix would be 132°
When the return gets up to 160F, 180SWT the return to to the boiler is 170.F
So return is blending up, dropping boiler efficiency a bit compared to a 160F return, that you would see if the system was running a 20∆.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream
trainer for Caleffi NA
Living the hydronic dream
0
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements