Help programming thermostat
Frankfog2
Member Posts: 35
Hey,
I need help properly programming the indept part of the thermostat. I have a Steam Boiler, they are balanced and function overall well. I had to replace the thermostat because it wasn’t turning the boiler on when it was supposed to. How do i set it up for steam heat? according to the manual default is set for forced heat.
https://www.honeywellstore.com/store/images/pdf/rth6360d-5-2-programmable-thermostat-manual.pdf
I need help properly programming the indept part of the thermostat. I have a Steam Boiler, they are balanced and function overall well. I had to replace the thermostat because it wasn’t turning the boiler on when it was supposed to. How do i set it up for steam heat? according to the manual default is set for forced heat.
https://www.honeywellstore.com/store/images/pdf/rth6360d-5-2-programmable-thermostat-manual.pdf
0
Comments
-
I have the same thermostat, mine is set up as follows
120- 0 (programmable thermostats are apparently not recommended in steam systems, that’s what my service guy told me)
125-0
200-3
205-12
Everything else i believe doesn’t apply, unless you’re using the thermostat for cooling as well in which case idk how to program that side0 -
Go into SET UP mode
once in setup mode scroll to number 200 and select 3 for boiler
then to item 205 and select item 12 for steam
If you want to use the setback feature, I would not set the night or away temperatures more than 5° lower than the at home temperature. But it would be better if you just left item 120 set at 0. Most steam systems are oversized and will recover quickly. But I seldom see any great savings on fuel usage. I would only use it for comfort reasons. Like if you want the room colder when you sleep.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 912 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements