Upgrading gas lines for new Rinnai rsc199ip tankless
jtboswell
Member Posts: 1
I am installing a new Rinnai rsc199ip tankless heater.
Currently, the house has two gas appliances and is fed by all 1/2 pipe. From the tank to the 2nd stage is black schedule 40 1/2"... then the same stuff runs into the house. From there it branches to Home Flex csst 1/2" to feed the stove and dryer.
Attached is a chart showing the proposed run.
I'm looking for insights on how to size the new lines. I'm sure I need to upgrade the 1/2" line from the tank and get a new 2nd stage regulator (it is from 1994!).
Your thoughts on sizing for each stage of the run?
Currently, the house has two gas appliances and is fed by all 1/2 pipe. From the tank to the 2nd stage is black schedule 40 1/2"... then the same stuff runs into the house. From there it branches to Home Flex csst 1/2" to feed the stove and dryer.
Attached is a chart showing the proposed run.
I'm looking for insights on how to size the new lines. I'm sure I need to upgrade the 1/2" line from the tank and get a new 2nd stage regulator (it is from 1994!).
Your thoughts on sizing for each stage of the run?
0
Comments
-
What PSI does your 2nd stage reg provide to the house piping?
If it is 2 PSI then each appliance would have it's own regulator to drop the 2 PSI down to 11-13" WC.
IMO, 1/2" is plenty for the 10 PSI between the regulators. I used to run 3/8" OD copper UG quite a distance from tank reg to house reg.0 -
If you have 10psi from the tank regulator to the house regulator and 2psi from the house regulator to each appliance, then 1/2" inch pipe is good for everything including the new water heater0
-
I would add that many modern gas appliances need a decent volume of gas immediately at ignition, if each appliance has its own regulator you may have issues if the gas pipe is only a short run from the appliance reg to the appliance. Many manufacturers I have spoken with have recommended at least 10' , though I have had several experiences where we needed a bit more than that.0
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 100 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 101 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 934 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements