Purging Air from radiator - are these the valves I use?
Comments
-
Air will rise up to the highest points of the system. This would usually be the radiators.
Do you have cast iron rad or baseboard convectors?
If you first check that you have 12-15 PSI in the system, then to to the heat emitters and open the air vents on them.
You may have to turn your tstats up to open the zone valves to allow the fill water to rise up to the upper levels.
If baseboard, there should be an air vent valve under the end plate, usually only one end.
If CI there would be an air vent on one end.
Post pictures if you can.0 -
Thanks - I've got baseboards, not one bleed valve on any of them. I'm guessing the bleed valves in the pic replaces what would be on the baseboard radiators. But being so small and so low (basement) on the return run, I don't see how the air could get forced down to the bleed valve. Does that setup look familiar?0
-
Baseboard air vents are not visible from the outside. If you remove the end caps, sometimes not attached to the heater itself, you might see them.0
-
I'm guessing those are some sort of isolation valve based on the shape. Might be a Muller logo on the side?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Not sure what kind of valves those are or what the do. The drain has to be upstream of the shut off or balancing valve0
-
If you are up for an adventure, you could hook a garden hose to the system, carefully keep pressure below 30 psi, and blast the air out with a high flow rate.
The location of the circ is hampering air removal on its own. But if it has worked in the past..
Those unknown valves would be the only isolation valves I see in the pics. They all look like they have leaked or seeped in the past.
If you get tom major surgery, a valve like this Webstone in every line is the modern purge option. Get rid of the coin vent and those brass mystery devices.
The valve near the zone valve is a flow check, it should be screwed down, clockwise, to work properly. It looks like another leak potential if you start screwing with it.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thanks for the input. Definitely no bleeds on the radiators. I've been purging thru the one spigot you can see in a pic, on the left with the hose hanging off. Figure if other zones are closed the air has to go back up thru that return run. Many buckets! Getting air out but much to go. Heated it up a bit for pressure and to get the circulator pump moving. New auto-purge on the air scoop singing alot also! Previous owners saved alot of $$ on valves ;-)) Thanks again0
-
Our messages crossed here... not touching the flow checks, searched what those were. If our subject "valves" are indeed valves, I can't move 'em anyway. But you mention the circ pump in the way - yes, but that makes me think if I leave it off and cold it has isolated the returns from the boiler. Then I open the PRV (keeping under 30 psi) Thanks Bobhot_rod said:If you are up for an adventure, you could hook a garden hose to the system, carefully keep pressure below 30 psi, and blast the air out with a high flow rate.
The location of the circ is hampering air removal on its own. But if it has worked in the past..
Those unknown valves would be the only isolation valves I see in the pics. They all look like they have leaked or seeped in the past.
If you get tom major surgery, a valve like this Webstone in every line is the modern purge option. Get rid of the coin vent and those brass mystery devices.
The valve near the zone valve is a flow check, it should be screwed down, clockwise, to work properly. It looks like another leak potential if you start screwing with it.0 -
Enough for tonight tho - will pick it up manana and be ready for that 20 degrees!0
-
-
Do the 4 mystery valves have a screwdriver slot in the center?
If so then if that is rotated 90 degrees that would isolate that zone.
If the packing nut (about the size of a quarter) is loosened then the screw might rotate.
The intent may have been to isolate each zone with those and power purge thru the small air bleed vent above them.....perhaps a slow process.1 -
Agreed! I bet that's the function, but they feel seized up so I didn't want to push my luck. I power purged each zone and that did the trick. Just lots of water used. I appreciate all the input ! Thanks!!!JUGHNE said:Do the 4 mystery valves have a screwdriver slot in the center?
If so then if that is rotated 90 degrees that would isolate that zone.
If the packing nut (about the size of a quarter) is loosened then the screw might rotate.
The intent may have been to isolate each zone with those and power purge thru the small air bleed vent above them.....perhaps a slow process.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements