Radiant Heat Pump
Mikb1957
Member Posts: 12
I'm trying to come up with the right circulator pump for my set-up. I have a cast iron oil-fired boiler with two zones, upstairs and downstairs baseboard. I eliminated the upstairs baseboard and have put in a five zone radiant heat manifold with zone valves. Four zones upstairs and one for the near future in backyard work shop. Longest zone is 300', all 1/2" pet. I have a Taco 5004 c-3 mixing valve. Trying to figure out the right circulator pump to use...Taco tech support said 0034e, a plumber off top of his head said 0010..any suggestions?
0
Comments
-
Both of those are way bigger than necessary. But the bigger issue here is piping, now that you're going to low temp. Does the boiler have a primary or bypass loop to assure return temps over 140* and prevent short excessive short cycling? Why does the upper level have 4 zones when it used to only be 1?0
-
Mikb .
Why do you have a DHW mixing valve on a heating system ? The valve you have is meant specifically for a pressure system , not a heating system . look at the chart I am attaching , every PSI represents 2.31 feet of resistance , that's why they recommended the large circulator .
You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330 -
5 loops at .50 gpm each is 2.5 gpm
300’ loop of 1/2 is 3’ of head
Add a foot for any piping and that becomes the pump spec. 2.5- 3 gpm at 4-5’ head
About the smallest circ you can buy should cover that
The circ needs to pump away from the mix port
The valve should work fine at that low flow rate. Lowest setting is 85 degrees
https://s3.amazonaws.com/s3.supplyhouse.com/product_files/Taco - 5004-C3 - Install Instructions.pdfBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Rich 49,
I checked with Taco tech support. They say the valve is the same exact one as the radiant heat only valve. Only difference is 5004 c-3 is rated for DHW (lead free). Thx.0 -
GroundUp,
I went from one zone on upper level to 4 because it had one loop of baseboard. My new set up is four rooms on their own thermostats, piped with 1/2 pex, each run between 200-300 ft.
As far as the piping, I've been researching that, and have found some information and diagrams showing two tees close together with a second mixing valve.. trying to find a diagram with my set-up.. baseboard on main level and the upper level with the radiant heat manifold. I am replacing the upper level CP with one mounted after the mixing valve and before the radiant manifold. Thx.0 -
Mikb . Well that's real nice , however it's still not the correct valve for the job . Look at the chart , figure how many gpm you require then figure out the head loss of the circuits . The Cv on the radiant mixing valve is 2.3 which means 2.3 gpm will impart 1 psi pressure drop through the valve . The radiant heat setpoint I Series has a Cv of 7 . Be careful also because Cv is not linear , it's exponential .
You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330 -
great that you're taking the time to size the circulator for intended duty. Contact taco tech support for help with sizing, and go with what will work without oversizing pump to minimize any velocity issues.
Taco tech support is 401-942-8000Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions1 -
Rich 49, I get what you're saying now, thanks for the heads up.0
-
5 loops of 1/2" pex, call it 3 gpm total.
Thru a 2.3 Cv thermostatic valve, here is what the pressure drop would be.
Just under 4' of head. Still within a typical small wet rotor circulator.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
With all due respect BOB . Where does the 3 gpm number come from , since when do we take SWAG on someone's question ? He has 5 loops of now and future radiant and a baseboard zone whose requirements we do not know , but venturing a guess since that's apparently what we're doing mine would be a minimum of 1 gpm since that's how baseboard is rated . What if these loops require 1 gpm and then we end up with a 7 gpm need . You will have given this man bad advice . Instead of having to be right maybe just give the advice needed for someone to figure it out and do it themselves . To be clear , it is my belief that your numbers are a fairy tale and may not work for this man , shame on you .hot_rod said:5 loops of 1/2" pex, call it 3 gpm total.
Thru a 2.3 Cv thermostatic valve, here is what the pressure drop would be.
Just under 4' of head. Still within a typical small wet rotor circulator.
You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330 -
With great curiosity RICH what flow rate do you suggest for 300’ 1/2” pex radiant loops?
I read it as he has removed the fin tube and added radiant loops. I doubt he would need a mix valve on fin tube, 300’ 1/2” loops? Do you run thermostatic mix valves on fin tube?
The OP can clarify if he is running 1/2 radiant or 1/2” to feed fin tube baseboard
For radiant loops The Radiant Rad Pad suggests .6 gpm. Others may suggest .5 gpm
He indicated he had 4 radiant loops with a possible 5th to be added
5 loops X .6 gpm = 3. When I went to school
3 gpm is plenty workable with the 2.3 mix valve he has, as I showed above
Taco seems to agree, as does the manual that comes with the valve. Sounds like you disagree? And suggest a lowlead valve. Instead?
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
-
With great curiosity RICH what flow rate do you suggest for 300’ 1/2” pex radiant loops?
I suggest performing a heat loss and using the temp , gpm that are required at various outdoor temps BOB , that's what I suggest .
I read it as he had 2 zones on BB , one up and one down , well here is what he siad , " With great curiosity RICH what flow rate do you suggest for 300’ 1/2” pex radiant loops? " QUOTE .
Systems SHOULD work well and as designed through a large range of ODTs and SWTs , BOB . You know this , and stop using formulas for 60* fluid .
I just looked at a recent design , a loop is 300' exactly , 12 " spacing 150* SWT , 20* Delta , .7 gpm and the head is 3.2 . So if someone required .7 gpm at a 10* Delta what would the head be . Nobody even asked where is this , what is design day conditions . None of it yet you're spouting off advice that may or may not be good . I suggested a valve specifically for heating systems .
You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330 -
-
-
The 40% glycol needs to be factored in the pump selection also.Mikb1957 said:Thank you all for the discussion
A quick read on sizing circulators here.
https://www.caleffi.com/sites/default/files/media/external-file/Idronics_16_NA_Circulation in hydronic systems.pdf
Rich is correct, the pump gets sized to the load of the system you connect to. That is the exact answer.
The figures I show are for typical 1/2" radiant loops, 300' with plain water. Your job could require less or more flow (gpm) than that quick calculator shows. As per the RadPad, 1/2" loop at .6 gpm, 12" on center spacing would give you an output around 22 BTU/ sq. ft.
Tighter tube spacing, higher flow rates are ways to get more output. realistically 25 or so btu/ sq ft is about what you get from a comfortable radiant floor. Surface temperature around 82F. Any warmer and the floor becomes uncomfortable to walk on in bare feet.
I was kidding about needing a $1000 circulatorBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
That's a relief0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements