Radiator feed and return on same side (feed on top) (return on bottom)
another question-
my boiler feeds a 3/4 line then I reduced it to he oxygen barrier 1/2 per then tees off to feed each radiator, in my case only 2 rads per zone
. then 1/2 pex returns both tee together but before returning to hot water heater it jumps back up to 3/4. I know you can size down while feeding but what about sizing up when returning ? I am by no means a professional but it seemed like a simple set up and im learning a lot as i go . please any insight on the matter would be great , I'll post some photos of what I mean on the return lines, im hoping the way I set it up it won't restrict returning water form rads - thanks !
Comments
-
to clarify its a tankless hot water heater navien system not a boiler.0
-
-
It doesn't sound like you have done a heat loss calculation as @EBEBRATT-Ed asks above.
Doing a heat loss calculation is your first step. Anything else done before that can have you working in circles.0 -
Heat loss is very minimal, one door, one fire rated door(to garage) on one zone , all spray formed and less then 150 sqft, with two oversized 8.5"wide 33" L radiators, (tucked in nooks) its an entry hallway/garage , also have the zone ran on a thermostat so wondering what kind of valves should be used on flow and return areas of radiators. Zone 2 is approx 300 sqft with two more the same size radiators with radiant heat above on next floor , (likely won't supplement heat but should help a bit , everything is spray foamed , including rim board above overhead, with one French door , new construction, caulked sealed, foamed around jams of doors all spray foamed.
My question is, is it worth running the piping, which will be visible, to the regualar ports of bottom left to bottom right , or keep it clean and route it directly off wall to flow in top of left side , return from both of left side how I originally ran it to fit existing radiators.
thank your for your time and input -Pete
0 -
yes they were originally fed top left feed, then return at the bottom left . That's why I ran the pex the way I did to begin with , shouldn't have jumped the gun on the design im thinking . I woudent mind routing the pipe to the standard bottom left to bottom right , may have an industrial look I just want to make sure the system runs efficantly. also curious if 1/2 he pex will do the job with these big a** radiators lol ?\! thanks again for your imput its highly appreciated ,im a carpenter not a plumber !EBEBRATT-Ed said:I would feed them the way they were originally fed or diagonally. I would not go bottom bottom. The pipe size you need is dependent on the size of the heat output you need for the room. Have you done a heat loss?
0 -
I did radiant heat on the floor above and had a company calc out and do heat loss for me , (radiant tec) never hired them or paid but used there calculations via email ) such a small area downstairs I am most defiantly overkilling the space, just trying to get the system working the best way possible, I I can run them traditionally but would have to remove the gaskets and refit them to run bottom to bottom , they are set to run top left feed and bottom left return for some odd reason . wounding mind doing that just seeing if its worth it , when im already overkilling , if I lose 5 % efficancy so be it , not worth spending the time and money for more pipe to run them bottom to bottom , thank you for your timeIntplm. said:It doesn't sound like you have done a heat loss calculation as @EBEBRATT-Ed asks above.
Doing a heat loss calculation is your first step. Anything else done before that can have you working in circles.0 -
yes I think ill do top left feed to bottom right return and run the pipe behind radiator hidden so I have a diagonal feed and return I've heard from other forums its best but debatable . only because I see all standard rads ran bottom to bottompjohn1993 said:
yes they were originally fed top left feed, then return at the bottom left . That's why I ran the pex the way I did to begin with , shouldn't have jumped the gun on the design im thinking . I woudent mind routing the pipe to the standard bottom left to bottom right , may have an industrial look I just want to make sure the system runs efficantly. also curious if 1/2 he pex will do the job with these big a** radiators lol ?\! thanks again for your imput its highly appreciated ,im a carpenter not a plumber !EBEBRATT-Ed said:I would feed them the way they were originally fed or diagonally. I would not go bottom bottom. The pipe size you need is dependent on the size of the heat output you need for the room. Have you done a heat loss?
0 -
any imputt on jumping from 1/2 pex to 3/4 on the returns ? do I need balancing valves ? not so sure about the set up on the returns !im in New Jersey and we do see some below freezing temps for weeks on end , sir making sure 1/2 pex will handle the job with such large rads (8.5"w33"L)0
-
You're fine with the 1/2 pex . with what you've described 1 gpm will be more than adequate to heat the space . You should always do a heat loss though and NEVER again consult with Radiant Reck .You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38331 -
I have heard a few horror stories on this forum, radiant reck lol thats good ! , thank you Rich, from your experience, is it worth changing the radiator feed and return to bottom bottom ? or keep them as they were originally ran, top left feed and bottom left return . how much am I really losing to have to re fit the rads , thanks again! cheersRich_49 said:You're fine with the 1/2 pex . with what you've described 1 gpm will be more than adequate to heat the space . You should always do a heat loss though and NEVER again consult with Radiant Reck .
0 -
That piping arrangement should work fine, as long as the hot water enters at the top and the return comes out the bottom.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting2 -
what kind of valves are required on flow and return if the room already has a thermostat communication with the zone feed ?0
-
what kind of valves would you recommend on the feed and supply with this configuration if the room is already on its own thermostat communication with the zone, thank youSteamhead said:That piping arrangement should work fine, as long as the hot water enters at the top and the return comes out the bottom.
0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements