Help with Buderus 2107 Logamatic Control

Maximus
Maximus Member Posts: 2
Hi there, I have a question regarding the Warm Weather Shutdown (WWSD) on my heating system, equipped with Buderus 2107 Logamatic Control.
Here is the problem, I set the WWSD temperature at 12 c° so the heating system should work only under this outside temperature and not over, but even with 15 c° the heating system doesn't enter in summer mode and start heating the house without any needs because in the rooms is more than 22 c°, so I go on the heating room and set manually the summer time.
There is something that I can check, for example a delta in temperature ?
Thanks

Comments

  • Maximus
    Maximus Member Posts: 2
    No ideas ?
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    If you know how to use a meter abd can download the control manual, you could check it out, otherwise you’re going to need someone familiar with that control to come over and start troubleshooting.

    There was an error rendering this rich post.

  • neilc
    neilc Member Posts: 2,791
    edited October 2023
    cold draft blowing on the OA sensor (?)

    or sensor out of spec, does the boiler control show the OA temp?
    known to beat dead horses
  • Big Ed_4
    Big Ed_4 Member Posts: 2,980
    On the three buttons , use the auto one ...

    There was an error rendering this rich post.

  • Grallert
    Grallert Member Posts: 746
    I would check if the OD temp reading on the screen is the same as your setting. Check the OD sensor. When you set the control to summer does the issue go away?
    Miss Hall's School service mechanic, greenhouse manager,teacher and dog walker