Does the BFPV look like it needs replacing?
LTP_VT
Member Posts: 2
Caleffi Series 573 installed vertically on my Triangle Tube system. I can't tell what is on this but it looks like some sort of corrosion. I was able to remove some of it with a brass brush.
BFPV isn't currently leaking from the vent port and I haven't noticed any issues with the autofill valve.
Any thoughts? Appreciate it!
BFPV isn't currently leaking from the vent port and I haven't noticed any issues with the autofill valve.
Any thoughts? Appreciate it!
0
Comments
-
The fiber washers are seeping, it would be best to replace them. Send me your address and I will send a couple, use the private message function if you want, or bob.rohr@caleffi.com
We have changed the design to use o-ring seals now on that and many other product
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream3 -
Thanks Bob - went ahead and sent you a PM. Appreciate the reply.0