TACO ZVC 406 - Coupled zones?
jholivier
Member Posts: 4
I have a TACO ZVC 406 controller - hydronic radiant heat.
The issue I am facing is the following:
When the thermostat associated with zone 4 calls for heat, the T-stat and valve lights on the controller do not turn on unless zone 3 has already been activated (T-stats and valve lights on) with its associated thermostat. In other words, if zone 3 is on, zone 4 works perfectly. This observation makes me believe the zones are somewhat coupled—the same issue with zone 2 and zone 5. Zone 2 needs to be on for zone 5 to operate.
All zones work perfectly, but this weird association between zones makes them not operate individually.
Any thoughts?
The issue I am facing is the following:
When the thermostat associated with zone 4 calls for heat, the T-stat and valve lights on the controller do not turn on unless zone 3 has already been activated (T-stats and valve lights on) with its associated thermostat. In other words, if zone 3 is on, zone 4 works perfectly. This observation makes me believe the zones are somewhat coupled—the same issue with zone 2 and zone 5. Zone 2 needs to be on for zone 5 to operate.
All zones work perfectly, but this weird association between zones makes them not operate individually.
Any thoughts?
0
Comments
-
@jholivier Please give us a call at 401-942-8000 and ask for Technical Services. We are here until 5pm EST.0
-
Thanks, Steve, I Already called your Technical Services, but the tech had no idea where this coming from.0
-
Please call and ask for myself, Steve in Tech Services
0 -
Can start with a photo of the ZVC panel wiring and what kind of thermostats0
-
Thank you DKO, I will post this tonight!0
-
Hi Everyone,
Thanks to Steve, I was able to resolve the issue. I am posting what I did:
As suggested by Steve, I jumped the R and W on the zones that seemed to be associated with other zones. When jumped, both zones worked independently as they were supposed to. This led me to believe it was a wiring between the thermostats and the zone on the TACO controller. While a former owner or contractor labeled the W wires for each zone with stickers (in the TACO box), the R wires (coming from the thermostat) were not. This led me to the hypothesis that the R wires were ill-connected. Knowing that a Voltage of ~ 25V exists between the R and W for each zone on the controller, I disconnected all the R and W wires and troubleshooted each zone separately by only connecting the W and R wire for that specific zone on the TACO controller. I then went to the thermostat corresponding to that zone to check the incoming voltage (between the R and W). If the wiring was correct, the voltage reading should be 25V. Of course, if the R wire was incorrect on the TACO controller, no voltage could be read on the specific thermostat I was troubleshooting. Using this workflow, I re-wired all the thermostats independently. Every zone works fine and independently from each other.
I am far from an expert, but it seems that my thought process was appropriate and made sense.
I am happy to hear your thoughts.0 -
Glad I was able to help. Enjoy the rest of your day.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements