Injection tee spacing

Options
When injecting a boiler primary loop into a secondary loop I’ve been told to keep the branch of the tees no further apart then 3 x the pipe diameter. No further then 12” centre to centre. Recently I’ve had another journeyman informing me that spacing the tees further apart works better as it gives the secondary loop more area to scrub heat off the primary loop. I was of the understanding that if you spaced the tees too far apart that you will not get return flow back into the primary loop. 
Mad Dog_2

Comments

  • hot_rod
    hot_rod Member Posts: 22,200
    Options
    The tee spacing on P/S has to do with keeping the pressure drop as low as possible. The more distance between the more chance of ghost or induced flow. A close nipple, regardless of the pipe diameter.

    It has nothing to do with heat scrubbing, that is a new one on me, however.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Mad Dog_2kcoppjringelRich_49
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,573
    Options
    When you say "injection" I assume you're using a pump to do the injecting If that is the case i don't think the spacing is critical but i would keep it within 10" or so. Same thing if using a three-way valve.

    The only reason to keep the tees close is to prevent unwanted "ghost flow". If you think ghost flow is a problem, keep the tees close.

    On larger commercial jobs with large size pipe the tees are so large you can't keep them 12" or less center to center. These jobs still work fine. There is no magic to the 12" number.
    Mad Dog_2
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    edited October 2023
    Options
    Closer is better. Journeyman is wrong.
    You couldn’t possibly be on this site without reading a few of Dan's books-which explains it simply and perfectly.

    There was an error rendering this rich post.

    Mad Dog_2kcopp
  • hot_rod
    hot_rod Member Posts: 22,200
    Options
    Here it is in a visual.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,050
    Options
    Sounds like your Journeyman friend may be conflating the Air Eliminator (Microbubble Air  scrubber)  with P/S Tee distance.  His next stop on the Journey should be here.  All of us will benefit.  Cross-Training and an infusion of  new blood is a good thing!  Mad Dog 🐕 
    kcoppSTEVEusaPAAllislandradiant
  • MikeDurigon
    MikeDurigon Member Posts: 33
    Options
    Hot Rod. Your last drawings notes 4 x diameter, Interesting. Scrubbing is my piping slang 😁 as the injection flow is backwards to the building loop. I’m calling the boiler loop primary and the building loop secondary. Primary and secondary loops both have Grundfos pumps. Boiler pumps into a Calefi hydraulic separator. 
    Mad Dog_2
  • MikeDurigon
    MikeDurigon Member Posts: 33
    Options
    Correction on my late night post. There is actually 3 loops. Boilers pump into the hydraulic separator. The the hydraulic separator pumps into the building loop via injection tees. The building loop has pumps on its own.
    Mad Dog_2
  • hot_rod
    hot_rod Member Posts: 22,200
    Options

    Hot Rod. Your last drawings notes 4 x diameter, Interesting. Scrubbing is my piping slang 😁 as the injection flow is backwards to the building loop. I’m calling the boiler loop primary and the building loop secondary. Primary and secondary loops both have Grundfos pumps. Boiler pumps into a Calefi hydraulic separator. 

    It shows a maximum of 4 pipe diameters, less is fine.
    For threaded pipe I use a close nipple. For sweat a nipple to allow enough gap to solder.With a tee drill you can get them really close together.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Mad Dog_2
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,573
    Options
    @MikeDurigon

    You mentioned "injection flow is backwards to building flow"

    This does not sound right. can you post a sketch??
  • MikeDurigon
    MikeDurigon Member Posts: 33
    Options

  • MikeDurigon
    MikeDurigon Member Posts: 33
    Options

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,573
    Options
    From what I can make out from the piping diagram the piping looks fine to me. I am not seeing "injection flow is backwards to building flow".

    The spacing between the supply and return tees is not that critical with pumped injection in my opinion.
  • Rich_49
    Rich_49 Member Posts: 2,766
    Options

    Hot Rod. Your last drawings notes 4 x diameter, Interesting. Scrubbing is my piping slang 😁 as the injection flow is backwards to the building loop. I’m calling the boiler loop primary and the building loop secondary. Primary and secondary loops both have Grundfos pumps. Boiler pumps into a Calefi hydraulic separator. 


    Boiler pump should pump away from Hydro Sep . If you have a Hydro Sep why do you have CSTs ?


    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
    Mad Dog_2