Viessmann gas valve
Harman009
Member Posts: 10
in Gas Heating
Had a viessmann b1ha lockout with an F4 fault indicating a lack of flame detected.
Got it back in action by adjusting the gas valve screw near the screen that says out with plus minus signs. Turning it higher brought the boiler back to life but now it's overfiring. Achieving 40c in low fire when it typically used to do 32.
Money is tight and gas valves are 500+ without labor and I don't have the proper tools to diagnose the issue properly. I did the basic steps from the viessmann videos but couldn't find the problem.
I am thinking a weak igniter or a problem with the gas valve. While I save up do you think its okay to leave it running how it is? Not in the heating season so currently it's just responsible for DHW via an indirect.
This will cause short cycling right? Also what does this screw do? Is there an startup ofset I can change instead?
I just want to make it last until my paycheck hits times are though. Although I rather have cold water than a blown up house
Got it back in action by adjusting the gas valve screw near the screen that says out with plus minus signs. Turning it higher brought the boiler back to life but now it's overfiring. Achieving 40c in low fire when it typically used to do 32.
Money is tight and gas valves are 500+ without labor and I don't have the proper tools to diagnose the issue properly. I did the basic steps from the viessmann videos but couldn't find the problem.
I am thinking a weak igniter or a problem with the gas valve. While I save up do you think its okay to leave it running how it is? Not in the heating season so currently it's just responsible for DHW via an indirect.
This will cause short cycling right? Also what does this screw do? Is there an startup ofset I can change instead?
I just want to make it last until my paycheck hits times are though. Although I rather have cold water than a blown up house
0
Comments
-
-
The throttle screw is only touched while doing a combustion test to adjust CO2 and 02 if needed. For all you know the boiler will soot now. You need a competent tech. Preferably someone familiar with Viessmann.
The only thing DIY for that boiler is maybe cleaning the igniter and flame sensor, and checking the drain and neutralizer.0 -
f4 is the lack of maintenance error code. You almost certainly have nothing wrong with the gas valve other than messing with that screw. You need a combustion analyzer to dial it back in correctly. But even before that a tech needs to check the incoming gas pressure, open the burner, clean up the whole heat exchanger, clean and inspect the condensate trap, and check out the igniter. Most of the time F4 is caused by a fouled up heat exchanger not allowing condensate to drain freely from the boiler. On rare occasions I have seen a bad ignition transformer, which requires a new board unfortunately as it is built in, on these instances it always came up as a repeated but intermittent fault. Viessmann has a 5 year parts warranty from the date of installation0
-
Okay thank you, I'll have a maintenance scheduled asap0
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 97 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements