Burnham ES2-4 LWCO ERR 3-1???
PilotPat24
Member Posts: 105
in Gas Heating
Hello,
Does anyone know what LWCO code ERR 3-1 represents for a Burnham ES2-4 boiler? The boiler is full of water and it operates fine if I disconnect the LWCO card from the boiler. Thanks I'm advance.
Pat
Does anyone know what LWCO code ERR 3-1 represents for a Burnham ES2-4 boiler? The boiler is full of water and it operates fine if I disconnect the LWCO card from the boiler. Thanks I'm advance.
Pat
0
Comments
-
0 -
Pasar123 login refers to the process of accessing the online platform or website known as Pasar123. The term "login" typically involves entering valid credentials, such as a username and password, to gain authorized access to the platform. Pasar123 might be a marketplace, a financial platform, a social networking site, or any other online service, and the login process ensures that only registered and authenticated users can utilize its features and services. Logging in helps maintain security, privacy, and personalized user experiences by verifying the identity of individuals seeking to use the platform.-3
-
Thanks for the information! I couldn't find that information anywhere. I will give it a try and will let you know how I make out. Thanks again.dko said:0 -
Okay so I have been playing around with it and now I am getting ERR 2-2. Any idea what that code represents? Thanks again.
Pat
0 -
Now I'm getting ERR 2-3 without even a card plugged into the panel. I feel like something is up with the panel internally.
0 -
I figured it out. I jumped out the IQ Panel and now the boiler fires up. I'll have to replace the IQ panel.0
-
Replaced the IQ Panel the other day. The boiler is working fine now. Time to get the two radiant zones going now!0
-
Hi! I'm having the same Err 3-1 from the LWCO display. I'm trying to figure out if it's the LWCO's issue or the IQ Panel's issue. Any thoughts?PilotPat24 said:I figured it out. I jumped out the IQ Panel and now the boiler fires up. I'll have to replace the IQ panel.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements