Rinnai Primary/Secondary Kit Required?
neoncrazy101
Member Posts: 1
Hello all, I'm not a professional HVAC guy but a DIYer. I have been in industrial maintenance though but this is my first time doing anything HVAC related.
I am replacing our 37 year old boiler with a new Rinnai i090SN wall mounted unit (non combi). I was doing an inventory of what I could use from my old system with the new system and ran into an issue.
On the old boiler it was a simple In and Out on the water piping with it being daisy chained throughout the baseboards/radiators (so no separate zoning per room) using a single circulating pump. I was reading in the manual for the Rinnai that it REQUIRES the use of a primary secondary heating kit or a low loss header. Do I really need that if its a single zone though? When I've searched online I keep running in to people having them installed with multiple zones but I couldn't find one with someone using it on a simple single zone and I would personally love not to have to spend $350+ on a kit if I don't need to.
Home is well insulated and 1300sq ft in NW Ohio with 2 radiators upstairs and everything else on the main floor.
I am replacing our 37 year old boiler with a new Rinnai i090SN wall mounted unit (non combi). I was doing an inventory of what I could use from my old system with the new system and ran into an issue.
On the old boiler it was a simple In and Out on the water piping with it being daisy chained throughout the baseboards/radiators (so no separate zoning per room) using a single circulating pump. I was reading in the manual for the Rinnai that it REQUIRES the use of a primary secondary heating kit or a low loss header. Do I really need that if its a single zone though? When I've searched online I keep running in to people having them installed with multiple zones but I couldn't find one with someone using it on a simple single zone and I would personally love not to have to spend $350+ on a kit if I don't need to.
Home is well insulated and 1300sq ft in NW Ohio with 2 radiators upstairs and everything else on the main floor.
0
Comments
-
All you need is two tees, maybe 30 bucks worth. Page 5 shows how to
pipe PS
The tees need to be close together maybe 2-4””
12” on either side of them
You still need a good air separator regardless
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
-
You'll be fine.. listen to the pros above...Rinnai is an excellent product. I have over a hundred out there...no issues..Great tech support 👏 mad Dog 🐕
1 -
cast iron rads, large piping, probably direct pipe.
unless you know or can measure flow rates.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
This is a do or don't question many "experienced" hydronic folk get wrong. There is a theoretical advantage to a well designed primary only piping application. No dilution and very low return temps with high delta T but it can go wrong quickly if all is not well thought out. If you have to ask, you should be piping it primary secondary. I've seen great single zone primary only designs go south because someone later on decides to chop them up into small zones with out p/s piping. Proper flow through the HX is a must. I think Rinnai has a don't even try it warranty policy. They don't want to have to vet designs of systems at all and I can't blame them. If you design for primary only, you must shoulder the liability for the potential efficiency gain. I have customers who trust my design and have efficient systems running at close to the wildly advertised but rarely achieved 94-95%0
-
The manual says you need to have hydraulic separation and there was even a tech bulletin put out when the i series came out. The plumbing kit sure saves a lot of time and gives it a clean look and ensures the piping is correct.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements