residio S8610U

Grallert
Grallert Member Posts: 834
Hello
I have a laars mighty therm, actually two. One has a Honeywell S8600 control where the pilot remains lit during the call. The 8610 drops the pilot right after the burners fire up and then they go out and the whole cycle starts over. Ignition, pilot, burner flame, off restart. Is there a way to set the 9610 for constant pilot? or is that even the issue? For all I know this has been going on for a long time but I doubt it. What am I missing? Any help would be greatly appreciated.
Thanks folks
M

Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver

Comments

  • Steamhead
    Steamhead Member Posts: 17,492
    Might be a bad flame signal. You really need a pro to fix this. Where are you located?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    Mad Dog_2
  • 109A_5
    109A_5 Member Posts: 1,909
    edited August 2023
    Hello @Grallert,
    Looking at the manual, I would say your 8610U unit is defective or wired wrong. OR !!! it is working correctly and there is not enough Gas pressure and/or flow to keep the pilot working with the main burner active. I suppose it could be a gas valve assembly issue too depending on the system.
    By your description I'm not sure if the system with the 8610U basically works OK for the whole call or it is continuously ignition cycling and you are not getting normal heat with that one unit.

    https://s3.amazonaws.com/s3.supplyhouse.com/product_files/Honeywell-S8610U3009-Install-Instructions.pdf



    Seems like the flame detection is probably working OK since the main burner fires.


    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    Grallert
  • dko
    dko Member Posts: 668
    The S8610U is not an OEM unit and is a universal replacement. Could you take a photo of the S8610U wiring and also of the control on the other unit.
    Grallert
  • JohnNY
    JohnNY Member Posts: 3,305
    On the 8600, does the pilot ever go out? Or could the pilot valve be stuck open?
    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
    Grallert
  • Grallert
    Grallert Member Posts: 834





    So here are some pictures of what I have. Checking pressures I have about 5+ inwg to the upstream side of both valves (two boilers). The wonky boiler shows 1-2 inwg to the down stream side of the valve I forgot to take a picture but as the one picture shows the funtioning boil has about 4inwg the the burner.
    The other valve is new out of the box from the supply house. I have to blame parts but I'm leaning that way.
    The wiring is as directed. The 8610U is the replacement for the 8600.

    Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver

  • Grallert
    Grallert Member Posts: 834
    JohnNY said:

    On the 8600, does the pilot ever go out? Or could the pilot valve be stuck open?

    The pilot does drop
    out just after the main burners ignite. Which made think control or wiring or a dip which. Didn't occur to me that gas pressure could be a culprit but I'm definitely not getting a good reading from that valve. (it's a new valve BTW)
    This all started because there was some serious roll out on this boiler I found a number of the burner tubes were blown out, They're replaced now.

    Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver

  • JUGHNE
    JUGHNE Member Posts: 11,311
    Is that pilot clean and does it have enough pressure?

    Or you could trade the spark/flame sensor from the good boiler and see if the problem stays with the boiler.
    Grallert
  • 109A_5
    109A_5 Member Posts: 1,909
    edited August 2023
    Hello @Grallert,

    Looks like you may have found the issue or an issue with the Gas pressure, maybe there is debris on the inlet of the gas valve assembly.

    If necessary and if you have not done so I would verify the wires go to the appropriate gas valve's terminals and their connections. You never know what the folks before you did.

    Also you could verify that there is 24 VAC still at the MV/PV to PV terminals when (the instant) the pilot erroneously goes out with the 8610U unit. The 24 VAC should go away when the 8610U unit determines the pilot is missing. Not sure what that delay time is (if any), maybe only a second or two.





    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    Grallert
  • Grallert
    Grallert Member Posts: 834
    Good advice! Thank you I'll verify 24, but in the meantime I've got a new valve on standby.

    Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver

  • Grallert
    Grallert Member Posts: 834
    ." I have" to blame parts " I just reread this. I meant to say I "hate" to blame parts!! Sometime new parts are bad but I hate to jump to that conclusion. I do have a new valve in the wings just in case. Good thing there are two if these boilers and one can carry the demand this time of year.

    Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,850
    If it's natural gas shouldn't you have 3.5" wc downstream of the gas valve?
    Grallert
  • Grallert
    Grallert Member Posts: 834
    The Boilers spec 4. the faulty boiler is only seeing 1to around 2 with no change after adjusting.

    Miss Hall's School service mechanic, greenhouse manager, teacher, dog walker and designated driver