Buderus GB142 heat exchangers

FB
FB Member Posts: 45
As a GB142 owner, I've read they are prone to heat exchanger failures. Are the failures from the inside-out or the outside-in? Every year I clean the white deposits off of the finned tubes using the mixture of mineral oil and water for soaking followed by reassembly, the "chimney sweep" cycle, disassembly, flushing with water, and repeat as needed. Does this cleaning prolong the HX life? And/or are there problems that develop inside the HX that eventually causes a failure?

Comments

  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,434
    Hi..How old is this install?  You're doing what you're supposed to do. Do you get a lot of buildup in the condensate trap?  The ones that I've seen fail wore down from the inside out and then leaked.  Any pictures?  Mad Dog 🐕 
  • hot_rod
    hot_rod Member Posts: 22,997
    Hows the water quality inside the boiler?
    Follow the manufacturers guideline for fill water, or glycol if that applies


    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream