Pressure relief valve leaking... any advice?

2»

Comments

  • mattmia2
    mattmia2 Member Posts: 10,962
    The cap seals off the outlet of the vent. It has to be loose for the vent to work. It will seal off the leak when it eventually leaks.
    edsut
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,408
    OP = Original Poster

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    Erin Holohan Haskelledsut
  • edsut
    edsut Member Posts: 45
    Ok, everything is installed. I opened up the valves, attached a hose to the hose bib on the return side and turned on the feed. I momentarily opened the PRV fast-fill to allow it to flow a bit faster. I shouldn't admit this, but initially after turning on the feed, hearing water flow and also hearing some air purge out of the vent I was concerned because there was no water coming out of the hose... Amazing what a difference it made after I opened that valve!! (motto: I'm an idiot) :-(
    Anyway, everything seems to have settled, so I shut off the hose valve and removed the hose. The feed is on, the two inline valves are open and the air vent remains open. I have a few [hopefully final] questions:
    • I adjusted the expansion tank to 12 PSI prior to filling with water, and now I see that it is up to about 13.5. The in-system gauge as well as the 2nd one I attached to the upper hose bib show a pressure about the same. Is that ok?
    • Do I leave the air vent in the open position all the time (my guess would be yes)?
    • I'm assuming it would be a good idea to turn the system on heat mode so that the pump engages and the system is in full-running mode for 30 minutes. Any reason not to do that?
  • mattmia2
    mattmia2 Member Posts: 10,962
    Leve the auto vent open.

    Run the boiler to get the water up to temp and help drive out the dissolved oxygen in the fresh water and move it to the vent.

    Not a terrible idea to turn the prv down a touch but 13.5 should be fine.
  • PC7060
    PC7060 Member Posts: 1,447
    edited July 2023
    Nice work!

    yes to all three! 

    Edit: quick fingers @mattmia2 beat me to the post. 
  • edsut
    edsut Member Posts: 45
    Thanks to all for the help on this! I saved a few $$ and learned a lot.
    Much appreciated!!
    EdTheHeaterMan