Found insulation stuffed inside boiler exhaust vent
2468ben
Member Posts: 12
After a nice father's day present of a burst indirect WH, local company made quick work of replacing it, until they turned on the oil boiler (buderus) and noticed the airflow was low. It's direct vent, through the wall, so they took off the vent hood outside... and found a bunch of sooty fiberglass stuffed near the end.
Like more than a square foot of batt shoved in the 4" pipe. The pipe is insulated, intact and the vent hood is screened, so the batt's too big to migrate from the wall, or get snuck in by an animal.
Trying to figure out why and when. Only other recent work--
1. Boiler tune-up in April, then guy came back the next day when the burner kept turning off after half a second. Adjusted something, said direct vents are weird sometimes and left. Only guy who's been servicing it for many years, but a man of few words so I never really understood the boiler cycle/venting until the WH tech explained it.
2. MassSave blew some cellulose in the eaves, and did a before/after blower door test. My best guess is maybe they unscrewed the exhaust pipe, plugged it and forgot to take it out later?
Or is this some secret New England technique for reducing condensation and icicles in a wall vent, and I gotta stuff it back in there by December.
Like more than a square foot of batt shoved in the 4" pipe. The pipe is insulated, intact and the vent hood is screened, so the batt's too big to migrate from the wall, or get snuck in by an animal.
Trying to figure out why and when. Only other recent work--
1. Boiler tune-up in April, then guy came back the next day when the burner kept turning off after half a second. Adjusted something, said direct vents are weird sometimes and left. Only guy who's been servicing it for many years, but a man of few words so I never really understood the boiler cycle/venting until the WH tech explained it.
2. MassSave blew some cellulose in the eaves, and did a before/after blower door test. My best guess is maybe they unscrewed the exhaust pipe, plugged it and forgot to take it out later?
Or is this some secret New England technique for reducing condensation and icicles in a wall vent, and I gotta stuff it back in there by December.
0
Comments
-
-
Is it fiberglass with binder or the pure white stuff? Could maybe a piece that got sucked/blown from the combustion chamber somewhere.0
-
-
So MassSave is an oxymoron in this instance.
Was the blower door test before or after the April tune up?
0 -
Field makes a blocked-vent switch for oil boilers:
https://www.supplyhouse.com/Field-Controls-WMO-1-Oil-Fired-Secondary-Safety-Kit?utm_source=google_ad&utm_medium=shopping_neutral&utm_campaign=Shopping_Neutral_New_users&gclid=CjwKCAjwv8qkBhAnEiwAkY-ahmXGW0TpVr-azIHCj-7eMI5ElEYX2hYBRiyoHYVMzk2hYOxYoAtMtBoCcEYQAvD_BwEAll Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Thought I'd give an update on the off-chance it matters -
MassSave came by for an inspection, sweared up and down they never touch the exhaust for a blower door test, and thought maybe it was malicious. If it was then they did a real crappy job, and based on our few conversations, the only person my boiler tech doesn't like is George Soros.
Only other thing I noticed is that before, in freezing temps I'd see a little steam outside from the direct vent during a run. When they took out the batt in May, they adjusted the boiler again and now no steam. I assume that's a good thing for a non-condensing boiler?1 -
-
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 419 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 59 Pipe Deterioration
- 920 Plumbing
- 6.1K Radiant Heating
- 374 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 40 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements