Lochinvar Armor Sputtering On Startup
Rizz861
Member Posts: 64
Just as the title says. Boiler is only a year or two old, it just got cleaned, gas psi was checked, and combustion test performed. Flame current is good (12.4mA) with new ignitor and flame sensor. I even called lochinvar to go over the issue and they had me tweak the low fire settings with no success. It is a member/leader setup and both boilers do it. They come on at 48% and sputter, but once they’re running they sound just fine. When I get into service mode and mess around with firing percentage, nothing causes this. I can start from low fire and go all the way to 100% and no issues. It only occurs when starting up. Lochinvar tech support was stumped and so am I. My guru at the supply house mentioned sagging pipes. That had me think about the install. I remember they tried to use a-bands on centrotherm pipe and the inspector nailed them and made them switch to those split rings with the rubbers. Getting split rings right with a pitched pipe and a ceiling that isn’t perfect can be a bear of a task. I’m wondering when they swapped the hangers they may have made some flat spots or spots that are pitched the wrong way. Have you guys seen sagging/bad pitched vents cause sputtering on any of your boilers you work on during startup only? This is the only thing that makes sense to me as I’ve checked all the boxes on usual suspects.
Check the condensate for clogging and backing up into the heat exchanger. Make sure there's an air gap between the boiler drain and pipe.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
“ Check the condensate for clogging and backing up into the heat exchanger. Make sure there's an air gap between the boiler drain and pipe.”It’s definitely not that as I serviced this myself. I believe it is the venting from what I’m hearing so I’m gonna check the pitch the next time I get out there. I will also take exhaust piping off to see if it does that noise.0
What are a-bands?
Swivel loop hangers?0 -
What size Boiler?
What is your altitute?
2" or 3" Exhaust Vent and how Long ?
Propane or Nat Gas?
Did you Clean the HX ?
Can you post the combustion results?
Did you clean the Venturi brass orifices?0
- 125 Chimneys & Flues
- 19 Recall Announcements