blow down cooler

tim smith
Member Posts: 2,841
Anyone come up with a simple solution to this for 2 million btu low pressure boiler for 50unit bldg. They are starting to bring this up on some jobs. Rather than a pretty expensive add on pre made cooler. Just searching for ideas. The inspector accepts alternate means or methods.
Thanks in advance
Tim
Thanks in advance
Tim
0
Comments
-
Any type of tank the blowdown water can sit in and seperate from the flash steam. Has to have a good vent to get rid of the steam. And a water regulating valve to put city water in to cool the condensate.
But this makes it an ASME issue at least on high pressure boilers. Low pressure I guess you may be able to get by with what the inspector accepts. But whoever insures the building may have an issue with it.0 -
thanks for input Ed.
Tim0