blow down cooler

Options
tim smith
tim smith Member Posts: 2,763
Anyone come up with a simple solution to this for 2 million btu low pressure boiler for 50unit bldg. They are starting to bring this up on some jobs. Rather than a pretty expensive add on pre made cooler. Just searching for ideas. The inspector accepts alternate means or methods.
Thanks in advance
Tim

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,574
    Options
    Any type of tank the blowdown water can sit in and seperate from the flash steam. Has to have a good vent to get rid of the steam. And a water regulating valve to put city water in to cool the condensate.

    But this makes it an ASME issue at least on high pressure boilers. Low pressure I guess you may be able to get by with what the inspector accepts. But whoever insures the building may have an issue with it.
  • tim smith
    tim smith Member Posts: 2,763
    Options
    thanks for input Ed.
    Tim