Vacuum Breaker on a Steam Heat Exchanger
KT1776
KT1776 Member Posts: 1
I have a client with a steam-to-hotwater converter that uses the building's central steam supply. The building's steam system operates with a vacuum pump return system. But there is a vacuum breaker installed on the steam supply inlet to the converter. My understanding is that you don't use vacuum breakers when you have a vacuum pump.
You can see the breaker on the top right of the picture.
    mattmia2 Member Posts: 17,478
    Knowing very little about commercial systems, isn't the vacuum only on the return if the steam traps are functioning properly?
    EBEBRATT-Ed Member Posts: 20,485
    When the steam control valve closes and there is steam in the heat exchanger a vacuum can form and not allow the condensate to drain this can cause water hammer and damage to the hx. If the traps are operating properly they should only open to pass condensate or air and close when steam is present.
    ScottSecorMad Dog_2
    109A_5 Member Posts: 4,209
    Mad Dog_2