Flat Plate heat exchanger system 200

I’m retired now but I have a friend in a town with fairly hard water with a 14 U heat exchanger for DHW. It’s about 15 years old and I doubt it’s ever been flushed. His DHW production is way down (he runs out during one long shower). Im guessing, since I’m not that familiar with this product, that the plate exchanger is clogged up and should be flushed or replace. Is this likely?
Mostly we installed gas boilers with Superstore indirects and I’ve only worked on a few of these systems.

Comments

  • Use what the HX manufacturer recommends; usually CLR (Calcium, Lime, Rust) or CitrusSurf 77.

    We use a transfer pump in a bucket along with the cleaner full strength.

    You may have to cut in some hose bibbs and ball valves to isolate the HX.

    Flush well afterwards to remove all traces of the cleaner.
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • SuperTech
    SuperTech Member Posts: 2,430
    After descaling the plate heat exchanger it would be a good idea to install an Aqua Pure AP431 scale stopper cartridge to minimize the potential for future problems.  Annually replace the cartridge and back flush the plate heat exchanger by closing the globe valve above the bronze circulator and opening the the drain valve above the valve and circulator.  
  • Big Ed_4
    Big Ed_4 Member Posts: 3,020
    I believe System 2000 uses a indirect storage tank ..

    You will have two circulator loops through the plate heat exchanger .

    The boiler and the Hot water loop . Check the flow though both . Check the flow with a hose . Just to note circulators have plastic spring checks built in today .

    If the plate HX is the problem , I would change it out and add a water filter on the cold water inlet to the plate HX






    There was an error rendering this rich post.

  • psb75
    psb75 Member Posts: 906
    The passages in a plate exchanger are "many and small." If they get clogged too badly, its best to put in a new unit. They are not that expensive, generally.
    Mad Dog_2
  • Big Ed_4
    Big Ed_4 Member Posts: 3,020
    Adding a set of valves to reverse flush the heat exchange is good practice

    There was an error rendering this rich post.

    Mad Dog_2
  • HVACNUT
    HVACNUT Member Posts: 6,338

    SuperTech
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,519
    I know the Systems 2000 is a pre-packaged rack system, so I'm not sure if you have room, but I always install Flat Plate HXs
    With 4  brass unions, 4 valves and 4 purge tees so I can flush in any direction and easily remove to soak in a decaying bath or hook up to a hose or air compressor.  Mad Dog 🐕