Replace hydrotherm with Gas boiler or High efficiency boiler

jack604
jack604 Member Posts: 3
I have a hydrotherm hc-135 boiler providing hot water to my radiant heating ( 7 zones, 2 zones in basement connected to poly b inslab, 5 zones connected to based board fin tubes). The boiler is working but my heating bills seem to be increasing during the winters. House insurance would like me to replace the boiler. Does it make financial sense to goto  a 95%+ efficiency boiler (navien, viessmen) or goto a gas-boiler 82% (raypak h135).


Comments

  • Hot_water_fan
    Hot_water_fan Member Posts: 1,823
    How many therms do you use per year?
    GGross
  • jack604
    jack604 Member Posts: 3
    Just added my bills, past year was about 2607 therms, this includes hydrotherm boiler, 40g hot water tank, BBQ and stove tops
  • Hot_water_fan
    Hot_water_fan Member Posts: 1,823
    Oh wow! That's a quite a bit. A high efficiency boiler works by using lower temperatures, which allows the gas exhaust to condense, thereby transferring more energy for the same input. Baseboard isn't the best for it, so there will be a portion of the winter when the baseboard portion won't be condensing. It depends on the heat loss to linear feet ratio: you might be condensing 99% of the year or much less. There are some other benefits to modcons - they're usually well fitted to the heat loss size compared to older boilers so there's less idle loss. The newer cast iron boilers can thermally purge, but their size is working against them still.

    There's no real "right" answer, both have pros and cons. However, you have a pretty favorable situation here due to your high gas usage.
    Mad Dog_2
  • Steamhead
    Steamhead Member Posts: 16,796
    @jack604 , first thing I'd do is get someone qualified to look at your present boiler and system. Something may be wrong with it that can be easily fixed. Where are you located?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    Mad Dog_2Derheatmeister
  • hot_rod
    hot_rod Member Posts: 22,024
    7 zones certainly favors a modulating boiler
    A heatload calculation would be a good start to determine the actual load.
    Could be the current boilers is oversized in addition to being low or mid efficiency. Does it run on an outdoor reset control? That too would help increase efficiency, on either type of boiler.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Mad Dog_2
    Mad Dog_2 Member Posts: 6,832
    As long as you are prepared to Do (or have a guy to do)  the annual maintenance on the Mod Con (a few hundred bucks a pop) that they ALL require,AND purchase a spare parts kit, (Great idea), The mod con WILL cut your gas bills.  Just make sure you don't have any gas leaks on the piping.  Many buildings small ones that  waste ALOT of gas, but you're not going to smell them.  Gave it checked also.  Mad Dog 🐕 
  • jack604
    jack604 Member Posts: 3
    Thanks you for all your responses.
    @steamhead I'm located in Vancouver Canada. Everyone that looks at it says that's old...they don't make it anymore. You've gotten your money's worth nad not much you can do if it's working.

    @hot_rod haven't done a heatload calculation, it was the one that came with the house when it was built. No outdoor reset that I'm aware of.

    @Mad Dog_2 what's annual maintenance of a mod con consist of? I annually bleed my system, change the thermocouple when needed and vaccum inside the burners, anything else a new mod con would need that a 35 yr old cast doesn't need.

    Also if I get a new boiler installed I'm considering replacing my dhw with either an indirect tank or go with instant dhw via a combi. Below is picture of my current set-up.
  • hot_rod
    hot_rod Member Posts: 22,024
    Those two combustion air ducts would go away with a mod on. Or combi upgrade. I suspect some heat goes out and cold air come in those vents, even when it required by the boiler or WH.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • walterk55
    walterk55 Member Posts: 2
    I seem to be using 600 therms per year. Most come from heating with my old HydroTherm 125B furnace. Even if I replaced that with a new more efficient furnace that is say 20% more efficient, the resulting saving of 120 therms per year might not justify the cost of the replacement furnace