Oil burner pressure goes up even if boiler is off
Izabela
Member Posts: 1
in Oil Heating
Please help! We are so lost! There is water that keeps on coming from the pressure release valve. We had a handyman come in today to change it. The psi dropped he left and we are now back with that same problem
psi went back up to 30 or over and the valve starts leaking again. The handyman has a surgery tomorrow and won’t be able to come in for few days. Any input is helpful
psi went back up to 30 or over and the valve starts leaking again. The handyman has a surgery tomorrow and won’t be able to come in for few days. Any input is helpful
0
Comments
-
-
Pressure builds when burner is off , you have a bypass . Either a bad pressure reducing valve or hole in heat exchanger . Shut off the pressure reducing valve as a test and if the pressure continues to rise it would be the hot water heat exchanger .I have enough experience to know , that I dont know it all0
-
If I may, I believe the post should read
Oil fired boiler pressure goes up even if boiler is off
Without more information I can only guess that this oil fired boiler also makes Domestic Hot Water (DHW). So if that is the case, there is the possibility that a heat exchanger coil from the DHW tank or DHW tankless coil is passing house water pressure to the lower boiler water pressure of the closed system.
In order to test the theory @Izabela would need to shut off the cold water feed to the DHW coil or tank. If the pressure stops increasing, then the problem is known. If the problem does not go away, then the automatic water feed PRV is defective. Close the valve to the automatic boiler feed to see if that results in pressure stabilization.
I hope this helps. If you need more help understanding this, we can help if you post some pictures of the boiler with all the pipe connections from different perspectives. High, low and angles.
Edward F Young. Retired HVAC ContractorSpecialized in Residential Oil Burner and Hydronics0
Categories
- All Categories
- 84.7K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 421 Carbon Monoxide Awareness
- 58 Chimneys & Flues
- 1.8K Domestic Hot Water
- 5K Gas Heating
- 124 Geothermal
- 158 Indoor-Air Quality
- 3.2K Oil Heating
- 57 Pipe Deterioration
- 830 Plumbing
- 5.6K Radiant Heating
- 373 Solar
- 14.3K Strictly Steam
- 3.1K Thermostats and Controls
- 55 Water Quality
- 42 Industry Classes
- 83 Job Opportunities
- 24 Recall Announcements