Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Whole home viessmann boiler

2

Comments

  • Mn1985
    Mn1985 Member Posts: 33
    mattmia2 said:
    Looking at the manual it could be controlled with a 0-10 v signal on what they call the "open therm" terminal from a building management system.
    On the 100-W b1he? 
  • mattmia2
    mattmia2 Member Posts: 11,011
    You could potentially make the air handler and the DHW make a DHW call and set that to a fixed higher temp and set a reset curve for the DH call for the radiant but I would push them to provide something closer to what they bid and refund the difference.
  • GGross
    GGross Member Posts: 1,312
    The DHW circuit is separated from the space heating circuit via a diverting valve inside the boiler. While you can get tricky with that it is not advised. I would push them to provide something closer to what you were quoted. The CU3A that was quoted would do what you want it to, and the 200 series would as well. I agree @Mn1985 that if the floor heat will be running the most you want the boiler to make that low temperature the majority of the time.
    mattmia2
  • mattmia2
    mattmia2 Member Posts: 11,011
    GGross said:

    The DHW circuit is separated from the space heating circuit via a diverting valve inside the boiler. While you can get tricky with that it is not advised. I would push them to provide something closer to what you were quoted. The CU3A that was quoted would do what you want it to, and the 200 series would as well. I agree @Mn1985 that if the floor heat will be running the most you want the boiler to make that low temperature the majority of the time.

    oh, so you must do dhw priority, you can't set it up however your system needs to be?
  • GGross
    GGross Member Posts: 1,312
    You could set it up to not use the separate tappings for DHW, but it's nice to keep that high temp separate from your low temp circuits if possible so I like to use the separate tappings. I see where you are going with this though, that you maybe could set the tank up as a zone, and if either the air handler or DHW calls the boiler would make high temp. It might work but I would not recommend it, because we are kind of fooling the control. One other quirk to point out, Viessmann uses a DHW tank sensor, and that helps the boiler fire as low as it needs to for DHW, if you just hook an aquastat to it, the boiler will fire at 194 F. We have actually used these for sanitizing lines at a dairy operation due to that extremely high temp. This is a feature I believe is only found in the current series boilers.
    mattmia2
  • Mn1985
    Mn1985 Member Posts: 33
    I think i found a solution. swap to 200 b2he and add thermostatic mixing valves to the radiant zones. put the house radiant on zone relay since they will all be same curve and has 3 separate zones and allows odr and thermostat control, put the air handler on non- mixed zone with thermostat, and garage radiant on heating circuit.

    Any thoughts on this setup?
  • Paul Pollets
    Paul Pollets Member Posts: 3,663
    edited April 2023
    are you exactly sure that the heatloss is identical on each zone? If it varies by more than 5-8 degrees, you should be using another mixing valve. And you'll get better performance using the Alpha 15-55 pumps, which can modulate to demand load. The DHWT can be a fixed rate pump, depending on tank size
    GGross
  • Mn1985
    Mn1985 Member Posts: 33

    are you exactly sure that the heatloss is identical on each zone? If it varies by more than 5-8 degrees, you should be using another mixing valve. And you'll get better performance using the Alpha 15-55 pumps, which can modulate to demand load. The DHWT can be a fixed rate pump, depending on tank size

    no, how would I calculate heat loss for each radiant zone?


  • Paul Pollets
    Paul Pollets Member Posts: 3,663
    This leaves HC1 as the air handler, HC2 the mixing valve and the DHWT as the circuits after the Low Loss Header
  • Mn1985
    Mn1985 Member Posts: 33

    This leaves HC1 as the air handler, HC2 the mixing valve and the DHWT as the circuits after the Low Loss Header

    dhwt direct from internal diverter valve.
  • Paul Pollets
    Paul Pollets Member Posts: 3,663
    Each circuit would have its own curve and the DHWT the temperature setpoint. If the piping and wiring diagram is followed that Viessmann provides in the installation manual, it will work with high accuracy. There will be a sensor in the LLH, the mixing valve, the DHWT and outdoors
  • Paul Pollets
    Paul Pollets Member Posts: 3,663
    Advanced heat loss calcs use proprietary software designed for radiant applications. LoopCad works well (and has a cost). The slantFin software is really for baseboard, not a radiant floor zone
  • Mn1985
    Mn1985 Member Posts: 33
    Update, boiler being switched to the 200 model and low loss header put in place. Thanks for everyone’s help in solving this 
    mattmia2Alan (California Radiant) Forbes
  • Allislandradiant
    Allislandradiant Member Posts: 38
    Send photos of the finished job.
    Mad Dog_2
  • tim smith
    tim smith Member Posts: 2,807
    Definitely a credit is in order for the downgrade of lesser boiler, no llh. Absolutely need of reset. I too if was doing viessmann would go the 200 not the 100 as Paul said, it has more capability. Bit sketchy not actually talking to you about contract change.
    Good luck
    mattmia2
  • Paul Pollets
    Paul Pollets Member Posts: 3,663
    The #100 is the economy model with no bells and whistles. It works best with 1 temperature. The #200 is designed for multiple circuit temperatures and has many features in the integral computer control
    GGross
  • Mn1985
    Mn1985 Member Posts: 33
    Still working on it. Should be finished tomorrow. Have not seen any mixing valves yet so should be interesting to see how they intend to have multiple temperatures if no mixing valves are added. 
  • Mn1985
    Mn1985 Member Posts: 33
    Update. Looks like instead of using mixing valves they just put the air handler zone on priority over the radiant zones. Thoughts? 
  • Paul Pollets
    Paul Pollets Member Posts: 3,663
    The boiler can only make different temperatures if a mixing valve is installed and integrated to the boiler computer.
    mattmia2
  • Mn1985
    Mn1985 Member Posts: 33
    Here is the layout 
  • Paul Pollets
    Paul Pollets Member Posts: 3,663
    edited May 2023
    You're in Minnesota. You'll find any issues with the design and installation sooner, rather than later. Unfortunately, they occur on the colder days of the year. If the heating curve is set for the air handler, the radiant zones will be too warm. If the curve is set for the radiant floors, the airhandler will be too cool. The boiler only recognizes different heating circuits and their respective temperatures by using a mixing valve proprietary to the boiler computer. It will also do an Indirect DHW tank with sensor on priority.
    mattmia2
  • Mn1985
    Mn1985 Member Posts: 33
    Boiler does have different heating curves the for floor zones and air handler. Floor zones won’t run if air handler is calling for heat. 

    Really thinking it should have computer controlled mixing valve on radiant but thinking maybe just a mixing valve on them to limit temp to radiant and not have air handler on priority 
  • mattmia2
    mattmia2 Member Posts: 11,011
    Mn1985 said:

    Really thinking it should have computer controlled mixing valve on radiant but thinking maybe just a mixing valve on them to limit temp to radiant and not have air handler on priority

    That is how it has to be set up. The mixing valve has to limit the temp to the radiant zone. Turning the setpoint of the boiler down doesn't instantly make the water in the system a safe temp for the radiant. Priority won't work for the air handlers because both zones will be calling for long periods of time if the curve is set up right. Priority for dhw only works because dhw calls are short and infrequent.
    GGross
  • GGross
    GGross Member Posts: 1,312
    I thought in the previous photos there was a manual style mixing valve installed? is that not there anymore? Forgive me it has been awhile and maybe this mixing valve serves another purpose. systems set up with a motorized valve are often ideal, I do like the manual style valves as an easier to deal with option if something were to break.


    mattmia2
  • Mn1985
    Mn1985 Member Posts: 33
    GGross said:
    I thought in the previous photos there was a manual style mixing valve installed? is that not there anymore? Forgive me it has been awhile and maybe this mixing valve serves another purpose. systems set up with a motorized valve are often ideal, I do like the manual style valves as an easier to deal with option if something were to break.  Correct. That is for the garage radiant zone. They removed that and have not finished that portion yet. 

    You made a good point of not running on priority because I’m afraid the radiant will never run. These are decisions of the contractor. 

  • hot_rod
    hot_rod Member Posts: 23,459
    You can do a proportional mix control with manual mix valved. Set the boiler up for the highest temperature load, on ODR

    then set the manual  valves at design temperature, so their temperature floats along the odr curve at the mixed down temperature

    Sn actuator could be added later if you want tighter control.

    for actuators you just need to know what signal the boiler sends out, 0-10vds or PWM for example

    one limitation is the mixed down circuits need to be a single zone, you could not add zone valves on the low temperature as it is a flow control mixing

    it is an inexpensive way to get a 3 temperature system all on odr

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2Mad Dog_2
  • GGross
    GGross Member Posts: 1,312
    As a bonus the boiler you have will accept up to three separate calls for heat, each with their own setpoint temp or ODR heating curve. The boiler will only be able to make the highest temp that is called for at any given time, but if you only have a call for low temp the boiler will only fire at the set temperature for that low temp call
    Mn1985
  • heathead
    heathead Member Posts: 238
    Gross,

    That is a great option I hadn't thought about. One could set it up with a two stage thermostat to make the boiler run the lowest curve most of the time, the low end of things and if it was too low the upper curve could take over to catchup in stage two. Or use one set for a vacation heating curve and one for a regular heating curve. That would save the most money by lowering the curve to match required load when it drops, when the house is not occupied for long periods of time.
  • Mn1985
    Mn1985 Member Posts: 33
    I asked them about no mixing valves and this is what I was told. 

    That boiler is a multi temp boiler.Air handler is set as priority with high temp.Floor zones are secondary at low temp.Nick from Viesmann set this up for us and all was working well when he left.
    For garage zone,plate exchanger is here,manifold should be here any day.Does Thursday the 25th work for this week?
    Thank you,
  • Paul Pollets
    Paul Pollets Member Posts: 3,663
    Let us know if you're able to get the system to respond at the right temps required without further modifications.
    mattmia2
  • mattmia2
    mattmia2 Member Posts: 11,011
    you might want to have a little private conversation with nick from viessman about if the boiler is installed as recommended
    GGross
  • Paul Pollets
    Paul Pollets Member Posts: 3,663
    I'd be very surprised if this doesn't become a boondogle. I've worked on hundreds of Vitodens boilers and know that if manufacturer's design specs for near-boiler piping and controls are not followed for multi temp systems, problems can be expected. I hate to be a downer but something's wrong with this setup.
  • Mn1985
    Mn1985 Member Posts: 33
    I'd be very surprised if this doesn't become a boondogle. I've worked on hundreds of Vitodens boilers and know that if manufacturer's design specs for near-boiler piping and controls are not followed for multi temp systems, problems can be expected. I hate to be a downer but something's wrong with this setup.
    This is why I turned to this site to get additional recommendations. Waiting to hear the reps explanation.

    every piece of literature from viessmann shows mixing valves when multi temps are used, even the tech seminar on the boiler explains it in detail. 
  • Allislandradiant
    Allislandradiant Member Posts: 38
    I be be late to the party, but how are you controlling the low temperature zones? Air temperature or slab temperature?
  • hot_rod
    hot_rod Member Posts: 23,459
    Call Viessmann tech support and ask for Bruce Faul or Pete the Heat. They are both long time contractors and reps in Colorado with V experience and they are tech support for Viessmann now.

    As I understand the Lochinvar 3 temperature you can only do one temperature at a time. Unless you add mixing devices. I don't see how the Viessmann would differ.,
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    GGross
  • Mn1985
    Mn1985 Member Posts: 33
    I be be late to the party, but how are you controlling the low temperature zones? Air temperature or slab temperature?
    Air temp 
  • Mn1985
    Mn1985 Member Posts: 33
    Here is local rep 

    Not certain who recommended it, but it was the way I programmed & currently would be the most efficient way to operate the boiler as you are not producing hotter water and mixing down for your low temperature zones.  Radiant floor can be without heat for around 45min-1 hour without noticing a difference in temperature, typical AHU call last 6-8 min.

     

  • GGross
    GGross Member Posts: 1,312
    I'm sorry that rep is mistaken. The low temp zone in this case needs to have a mixing valve, it doesn't have to be a motorized mixing valve, but it must have a mixing valve (motorized is best). So it sounds like they are turning off the pump to the low temp zone while the high temp zone is calling? This is not the correct way to set up this system. This is either a case of the rep actually not understanding how this system should function, or they are afraid to tell the contractor to fix it.

    How do they know the typical AHU call is 6-8 minutes when the system hasn't been started up yet?

  • dko
    dko Member Posts: 668
    The rep sounds like he is under the impression the AHU and radiant are running at the same temperature.
  • Mn1985
    Mn1985 Member Posts: 33
    Additional info from rep 

    The AHU would have never shutoff would only be the way your RFH would get starved, typical AHU/Furnace run around 6-8 min then it will switch to your RFH should be a great system, this is how I program all our IBC Boilers too and have never had an issue.