Am I maxing out the venting capacity of the 1/2" pipe with a single BM and adding another was unnecessary ? After a few years of the single vents config I attached a backup extra to one side in January and felt like It made a difference, so I did it again.
also the ward reducing 45 street leg is a beautiful fitting
also the ward reducing 45 street leg is a beautiful fitting
0
Comments
-
A half inch pipe can handle 4.8CFM at 3oz of pressure so it probably won't allow two BigMouths to vent completely but it will do better than a single B&J..
Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Agreed, one B&J Big Mouth can pass 3.6CFM. I didn't see a number in the Pajak report, but found it on Amazon (I know, that's not necessarily the most reliable source, but the number seems reasonable).0